[Equest-users] daily occupancy schedules
Nick Caton
ncaton at smithboucher.com
Tue Apr 13 14:09:16 PDT 2010
Stephen,
In a word, yes - and suggesting you do it in the detailed mode.
As a simplified approach for your example (you might want to define more
detail), you might start with 3 fractional occupancy "Day" schedules:
1. Regular Day (7-9 only)
2. Evening Day (7-9 and 6-8)
3. Sunday Day (Sunday worship hours)
Then, create 1 week schedule and assign the above day schedules to each
day of the week/holidays as may be appropriate:
Mo - Regular Day
Tu - Regular Day
We - Evening Day
Th - Regular Day
Fr - Evening Day
Sa - Regular Day
Su - Sunday Day
Holidays - Sunday Day
For the annual occupancy schedule, assign the same week schedule to
every week in the year.
Wrap up by assigning your new annual occupancy schedule to the
appropriate space(s) (right click any space in the Component Tree/2D
view/3D view under the Internal Loads tab).
When you have many custom schedules to define, I think the best approach
is to use the wizards to set up your holidays and seasonal building
operating schedules as appropriate, then use the detailed mode to
create/assign new schedules in a way that helps you to find/keep track
of your work. It's technically possible to define a fractional
occupancy schedules for every zone for every hour of the year (limited
only by the user's time/sanity, of course).
Occupancy schedules can be handled entirely in the wizards if you have
one schedule per shell.
A BIG caution: I made the mistake once of creating many small shells
(>12 - large project) in the wizards for the express purpose of avoiding
dealing with custom schedules in detailed mode (as I hadn't done it
before) - this was a bad move! The time "saved" by this approach was
completely engulfed by the time lost wrangling in the detailed mode with
the resulting overly-complex model.
Best of luck,
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Stephen
Sorensen
Sent: Tuesday, April 13, 2010 3:10 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] daily occupancy schedules
Hi everyone,
Does e-Quest allow for multiple usage schedules per day. For example, a
particular religious worship building is primarily used on Sundays, so,
that schedule is easy to enter, however, during the week, the building
is used every day from 7am-9am. The difficult part comes from the fact
that two nights a week it is used from 6p-8p. how can I get e-quest to
show this schedule irregularity?
Stephen Sorensen
Hansen Engineering
Friendsville, PA
P: 570-553-4284
F: 570-553-0234
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100413/d577eba7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100413/d577eba7/attachment.jpeg>
More information about the Equest-users
mailing list