[Equest-users] Equest space heating in summer
John Aulbach
jra_sac at yahoo.com
Tue Apr 13 10:18:00 PDT 2010
Burt:
Just a hunch.
In the Wizard, you do not (as far as I know) have the luxury of temperature reset schedules. Therefore, your heat is available 24/7/365. Your space heating loop is also on a continuous basis, rather than a Demand basis. Therefore, you are circulating space heating hot water to the perimter all the time, at some minimum value to keep the perimeter "ready."
Remove the perimeter heating (make the space unconditioned) and see if your Summer gas goes away. You can always send the .INP and the .PD2 files to the Forum. Someone ALWAYS knows a good answer.
Welcome to the Forum.
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
PartnerEnergy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com
________________________________
From: Burt <burt at mcaeg.com>
To: equest-users at lists.onebuilding.org
Sent: Mon, April 12, 2010 2:06:50 PM
Subject: [Equest-users] Equest space heating in summer
People of E-Quest:
I am new to the program and am using the Building Wizard. Have an existing one-story U shaped building with an area of 127,500 ft2. The perimeter is heated by hot water and the core is gas furnace heated by package rooftop heat/cool units. There is no reheat to the AC. There is a gas-fired DHW water heater and storage. The printout shows a significant space gas usage during the summer not including the DHW. The DHW approximates the actual DHW of the building. Does anybody have an idea what may be wrong? Hope you can help.
Burt Swerdling
The MC Alliance Energy Group, Inc.
VP Of Engineering
30 Crossways East
Bohemia, New York11716
email: burt at mcaeg.com
Making the World a GreenerPlaceOneBuildingat a TimeSM
The information contained in this electronic email transmission is intended only for the use of the individual or entity to whom it or to which it is addressed, and may contain information that is privileged, confidential and exempt from disclosure under applicable law. If the reader of this communication is not the intended recipient, or the employee or agent responsible for delivering this communication to the intended recipient, you are hereby notified that any dissemination, distribution, copying or disclosure of this communication is strictly prohibited. If you have received this transmission in error, please notify the sender and delete the original communication.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100413/364ec26a/attachment.htm>
More information about the Equest-users
mailing list