<DIV>Burt:</DIV>
<DIV> </DIV>
<DIV>Just a hunch.</DIV>
<DIV> </DIV>
<DIV>In the Wizard, you  do not (as far as I know) have the luxury of temperature reset schedules. Therefore, your heat is available 24/7/365. Your space heating loop is also on a continuous basis, rather than a Demand basis. Therefore, you are circulating space heating hot water to the perimter all the time, at some minimum value to keep the perimeter "ready."</DIV>
<DIV> </DIV>
<DIV>Remove the perimeter heating (make the space unconditioned) and see if your Summer gas goes away.  You can always send the .INP and the .PD2 files to the Forum.  Someone ALWAYS knows a good answer.</DIV>
<DIV> </DIV>
<DIV>Welcome to the Forum.</DIV>
<DIV> </DIV>
<DIV><BR>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><A name=_MailAutoSig><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>John R. Aulbach, PE, CEM<?xml:namespace prefix = o ns = "urn:schemas-microsoft-com:office:office" /><o:p></o:p></FONT></SPAN></A></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>Senior Energy Engineer<o:p></o:p></FONT></SPAN></SPAN></P>
<DIV style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #17365d; mso-fareast-font-family: 'Times New Roman'; mso-no-proof: yes"><FONT face=Calibri>
<HR style="COLOR: #17365d" align=left SIZE=2 width="30%" noShade>
</FONT></SPAN></SPAN></DIV>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><FONT face=Calibri><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: navy; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Partner</SPAN></B></SPAN><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: green; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"> </SPAN></B></SPAN><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: #006600; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Energy</SPAN><SPAN style="FONT-VARIANT: small-caps; COLOR: navy; mso-no-proof: yes"><o:p></o:p></SPAN></B></SPAN></FONT></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>1990 E. Grand Avenue, El Segundo, CA 90245<BR>W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745<o:p></o:p></FONT></SPAN></SPAN></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"></SPAN><A href="http://www.ptrenergy.com/"><FONT face=Calibri><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">www.ptrenergy.com</SPAN></SPAN><SPAN style="mso-bookmark: _MailAutoSig"></SPAN></FONT></A><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri> </FONT></SPAN></SPAN><A href="mailto:%7C%20jaulbach@ptrenergy.com"><FONT face=Calibri><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">| jaulbach@ptrenergy.com</SPAN></SPAN><SPAN style="mso-bookmark: _MailAutoSig"></SPAN></FONT></A><SPAN style="mso-bookmark:
 _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><o:p></o:p></SPAN></SPAN></P><SPAN style="mso-bookmark: _MailAutoSig"></SPAN>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><o:p><FONT face=Calibri> </FONT></o:p></SPAN></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><o:p><FONT face=Calibri> </FONT></o:p></P></DIV>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><BR>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><FONT size=2 face=Tahoma>
<HR SIZE=1>
<B><SPAN style="FONT-WEIGHT: bold">From:</SPAN></B> Burt <burt@mcaeg.com><BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> equest-users@lists.onebuilding.org<BR><B><SPAN style="FONT-WEIGHT: bold">Sent:</SPAN></B> Mon, April 12, 2010 2:06:50 PM<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> [Equest-users] Equest space heating in summer<BR></FONT><BR>
<STYLE>
<!--

filtered {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}

p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;margin-bottom:.0001pt;font-size:11.0pt;font-family:"sans-serif";}
a:link, span.MsoHyperlink
        {color:blue;text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {color:purple;text-decoration:underline;}
span.EmailStyle17
        {font-family:"sans-serif";color:windowtext;}
.MsoChpDefault
        {}
filtered {margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {}
-->
</STYLE>

<DIV class=Section1>
<P class=MsoNormal>People of E-Quest:</P>
<P class=MsoNormal>I am new to the program and am using the Building Wizard.  Have an existing  one-story U shaped building with an area of 127,500 ft2.  The perimeter is heated by hot water and the core is gas furnace heated by package rooftop heat/cool units.  There is no reheat to the AC.  There is a gas-fired DHW water heater and storage.  The printout shows a significant space gas usage during the summer not including the DHW.  The DHW approximates the actual DHW of the building.  Does anybody have an idea what may be wrong?  Hope you can help.</P>
<P class=MsoNormal> </P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 10pt">Burt Swerdling</SPAN><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 12pt"></SPAN></P>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 12pt">The MC Alliance Energy Group, Inc.</SPAN></B><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 12pt"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 10pt">VP Of Engineering</SPAN><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 12pt"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 10pt">30 Crossways East<SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 12pt"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; FONT-SIZE: 10pt"><SPAN style="COLOR: navy">Bohemia</SPAN><SPAN style="COLOR: navy">, </SPAN><SPAN style="COLOR: navy">New York</SPAN><SPAN style="COLOR: navy"> 11716</SPAN></SPAN></SPAN><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 12pt"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 10pt">email: burt@mcaeg.com</SPAN><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 12pt"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 12pt"> </SPAN></P>
<P style="TEXT-ALIGN: center" class=MsoNormal align=center><SPAN style="FONT-FAMILY: 'serif'; COLOR: gray; FONT-SIZE: 12pt">Making the World a </SPAN><SPAN style="FONT-FAMILY: 'serif'; FONT-SIZE: 12pt"><SPAN style="COLOR: #336600">Greener</SPAN><SPAN style="COLOR: gray"> </SPAN><SPAN style="COLOR: gray">Place</SPAN><SPAN style="COLOR: gray"> </SPAN><SPAN style="COLOR: gray">One</SPAN><SPAN style="COLOR: gray"> </SPAN><SPAN style="COLOR: gray">Building</SPAN><SPAN style="COLOR: gray"> at a Time<SUP>SM</SUP></SPAN></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 12pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 10pt">The information contained in this electronic email transmission is intended only for the use of the individual or entity to whom it or to which it is addressed, and may contain information that is privileged, confidential and exempt from disclosure under applicable law. If the reader of this communication is not the intended recipient, or the employee or agent responsible for delivering this communication to the intended recipient, you are hereby notified that any dissemination, distribution, copying or disclosure of this communication is strictly prohibited. If you have received this transmission in error, please notify the sender and delete the original communication.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; COLOR: navy; FONT-SIZE: 10pt"> </SPAN><SPAN style="FONT-FAMILY: 'serif'; FONT-SIZE: 10pt"></SPAN></P>
<P class=MsoNormal> </P></DIV></DIV></DIV></DIV></div><br>