[Equest-users] Active Chilled Beam/Fan Coil System

Greg Collins GCollins at glumac.com
Fri Apr 9 15:00:19 PDT 2010


Thanks to everybody for the interest and feedback so far..

 

Chilled water supply to the beams is 56F.  

 

I've attached my inp and pd2 files in case anybody wants a closer look.


 

Greg

 

From: Bruce Easterbrook [mailto:bruce5 at bellnet.ca] 
Sent: Friday, April 09, 2010 2:24 PM
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Active Chilled Beam/Fan Coil System

 

Maybe you are now running into what eQuest uses to prevent condensation
on the chilled beam coil.  Condensation would be allowed in the FCU as
it could/would have a drain tray.  Where the mixing takes place is
important on the chilled beam.  eQuest should consider the mixing takes
place after the coil and the warm humid air is entering the coil.  I
would think eQuest would be set up to prevent condensation on the coil,
you don't want water dripping out of the unit.  What is the temperature
of your chilled water supply?
Bruce

On 09/04/2010 04:32 PM, Greg Collins wrote: 

I have tried it, but I end up getting an error saying the leaving air
temp off the coil needs to be at least 6F higher than the entering water
temp to the coil, and for some reason I don't get the same error for the
FCU.  In an active chilled beam, the coil is actually just cooling the
room induction air, then mixing it with the primary air from the DOAS.
I think that equest assumes the air mixes before entering the coil,
which fundamentally is the same thing, but the numbers trip this error
message.  I'll look into more why the FC system doesn't make that
happen, but the two seem to be essentially the same system except for
the fan (which I make 0.000001 kW/cfm anyway).

 

From: Grando, John [mailto:JGrando at cosentini.com] 
Sent: Friday, April 09, 2010 1:00 PM
To: Greg Collins; Bruce Easterbrook
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Active Chilled Beam/Fan Coil System

 

Have you looked into SYSTEM TYPE = IU (Induction Unit).  This may be a
better path to try.

 


John Grando LEED AP| Mechanical Engineer


  

 

 

________________________________

From: Greg Collins [mailto:GCollins at glumac.com] 
Sent: Friday, April 09, 2010 2:00 PM
To: Bruce Easterbrook
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Active Chilled Beam/Fan Coil System

Bruce,

 

I agree with your theory and the justification, but the question is
ultimately "how to model it?"  I don't think you can put in negative
heat for a baseboard system, hook it up to a chilled water loop and get
results you can count on. 

 

Greg

 

From: Bruce Easterbrook [mailto:bruce5 at bellnet.ca] 
Sent: Friday, April 09, 2010 8:59 AM
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Active Chilled Beam/Fan Coil System

 

    I'm not totally up on using DOAS with eQuest or with chilled beams
being in Canada but it would seem to me the OA will have to be used to
control humidity in the space.  The chilled beam should not be used for
latent cooling, sensible only, to prevent condensation issues.  The DOAS
will need to control the dewpoint of the room air and maintain it below
the operating temperature of the coil in the chilled beam.  The chilled
beam would only be dealing with the sensible load from the space.  The
DOAS would do everything else.  The question would be will eQuest allow
a single zone AHU c/w economizer and a baseboard system with negative
heat?  I have never tried that with eQuest.
Bruce Easterbrook
Abode Engineering

On 08/04/2010 04:46 PM, James Hansen wrote: 

I'm interested in this as well - I know that in DOAS systems like active
chilled beams, the primary air often takes on a fairly large chunk of
space latent cooling, and if this can't be passed on from the DOAS
system to the space, then I don't see how we can believe the results.

 

GHT Limited
James Hansen, PE, LEED AP

Senior Associate

1010 N. Glebe Rd, Suite 200

Arlington, VA  22201-4749

703-338-5754 (Cell)

703-243-1200 (Office)

703-276-1376 (Fax)

www.ghtltd.com <http://www.ghtltd.com/> 

 

 

From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Greg
Collins
Sent: Thursday, April 08, 2010 4:39 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Active Chilled Beam/Fan Coil System

 

Hi all,

 

I'm working on modeling an active chilled beam system.  It consists of
the chilled beams and a dedicated unit to provide primary air (mainly
ventilation air) to the beams at 55 degrees.  I've modeled the chilled
beam system as a fan coil system, but am wondering about my options for
modeling the primary air.  

 

My question is this:  If I attach the primary/ventilation air unit to
the fan coil system in the FC's Outdoor Air tab under "Outside Air from
System" will the temperature of the air coming from that unit have an
impact on the load in the space?  I have a ton of hours at very low load
during the winter months, and I want eQuest to use the 55 degree primary
air as the first stage of cooling for the space and not "double up" the
cooling energy by cooling the 55 degree air and then not use that for
cooling in the zones.

 

If anybody has some input, it would be appreciated. 

 

Greg Collins
Design Engineer / Energy Analyst

Mechanical Department
LEED(r) Accredited Professional

  <http://www.glumac.com/> 

________________________________

NOTE OUR NEW ADDRESS

18200 Von Karman Ave., Suite 100
Irvine, CA 92612
T.  949.833.8190  F. 949.833.0252

Thinking. Inside the building.
www.glumac.com <http://www.glumac.com/>  

 

________________________________

The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee.  It is
the property of GHT Limited.  Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful.  If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments.  Thank you.

 
 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to 
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
  


NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if
any) are intended solely for the use of the addressees hereof. In
addition, this message and the attachments (if any) may contain
information that is confidential, privileged and exempt from disclosure
under applicable law. If you are not the intended recipient of this
message, you are prohibited from reading, disclosing, reproducing,
distributing, disseminating or otherwise using this transmission.
Delivery of this message to any person other than the intended recipient
is not intended to waive any right or privilege. If you have received
this message in error, please promptly notify the sender by reply E-mail
and immediately delete this message from your system. 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100409/708d03e8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 6582 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100409/708d03e8/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Madera Courthouse v3.2.inp
Type: application/octet-stream
Size: 334809 bytes
Desc: Madera Courthouse v3.2.inp
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100409/708d03e8/attachment.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Madera Courthouse v3.2.pd2
Type: application/octet-stream
Size: 2079 bytes
Desc: Madera Courthouse v3.2.pd2
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100409/708d03e8/attachment-0001.obj>


More information about the Equest-users mailing list