[Equest-users] Active Chilled Beam/Fan Coil System
Carol Gardner
cmg750 at gmail.com
Fri Apr 9 14:23:30 PDT 2010
Greg,
Three questions. Have you talked to Mitch in your Portland office? He's a
great resource but I don't know how things are at Glumac right now. Are
running your OA through a HRV, and lastly is your OA constant volume or are
you varying it?
Carol
On Fri, Apr 9, 2010 at 1:32 PM, Greg Collins <GCollins at glumac.com> wrote:
> I have tried it, but I end up getting an error saying the leaving air
> temp off the coil needs to be at least 6F higher than the entering water
> temp to the coil, and for some reason I don’t get the same error for the
> FCU. In an active chilled beam, the coil is actually just cooling the room
> induction air, then mixing it with the primary air from the DOAS. I think
> that equest assumes the air mixes before entering the coil, which
> fundamentally is the same thing, but the numbers trip this error message.
> I’ll look into more why the FC system doesn’t make that happen, but the two
> seem to be essentially the same system except for the fan (which I make
> 0.000001 kW/cfm anyway).
>
>
>
> *From:* Grando, John [mailto:JGrando at cosentini.com]
> *Sent:* Friday, April 09, 2010 1:00 PM
> *To:* Greg Collins; Bruce Easterbrook
>
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* RE: [Equest-users] Active Chilled Beam/Fan Coil System
>
>
>
> Have you looked into SYSTEM TYPE = IU (Induction Unit). This may be a
> better path to try.
>
>
>
>
> *John Grando** **LEED AP**| **Mechanical Engineer
> *
>
>
>
>
>
>
> ------------------------------
>
> *From:* Greg Collins [mailto:GCollins at glumac.com]
> *Sent:* Friday, April 09, 2010 2:00 PM
> *To:* Bruce Easterbrook
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Active Chilled Beam/Fan Coil System
>
> Bruce,
>
>
>
> I agree with your theory and the justification, but the question is
> ultimately “how to model it?” I don’t think you can put in negative heat
> for a baseboard system, hook it up to a chilled water loop and get results
> you can count on.
>
>
>
> Greg
>
>
>
> *From:* Bruce Easterbrook [mailto:bruce5 at bellnet.ca]
> *Sent:* Friday, April 09, 2010 8:59 AM
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Active Chilled Beam/Fan Coil System
>
>
>
> I'm not totally up on using DOAS with eQuest or with chilled beams
> being in Canada but it would seem to me the OA will have to be used to
> control humidity in the space. The chilled beam should not be used for
> latent cooling, sensible only, to prevent condensation issues. The DOAS
> will need to control the dewpoint of the room air and maintain it below the
> operating temperature of the coil in the chilled beam. The chilled beam
> would only be dealing with the sensible load from the space. The DOAS would
> do everything else. The question would be will eQuest allow a single zone
> AHU c/w economizer and a baseboard system with negative heat? I have never
> tried that with eQuest.
> Bruce Easterbrook
> Abode Engineering
>
> On 08/04/2010 04:46 PM, James Hansen wrote:
>
> I’m interested in this as well – I know that in DOAS systems like active
> chilled beams, the primary air often takes on a fairly large chunk of space
> latent cooling, and if this can’t be passed on from the DOAS system to the
> space, then I don’t see how we can believe the results.
>
>
>
> *GHT Limited
> **James Hansen, PE, LEED AP*
>
> *Senior Associate*
>
> 1010 N. Glebe Rd, Suite 200
>
> Arlington, VA 22201-4749
>
> 703-338-5754 (Cell)
>
> 703-243-1200 (Office)
>
> 703-276-1376 (Fax)
>
> www.ghtltd.com
>
> * *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [
> mailto:equest-users-bounces at lists.onebuilding.org<equest-users-bounces at lists.onebuilding.org>]
> *On Behalf Of *Greg Collins
> *Sent:* Thursday, April 08, 2010 4:39 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Active Chilled Beam/Fan Coil System
>
>
>
> Hi all,
>
>
>
> I’m working on modeling an active chilled beam system. It consists of the
> chilled beams and a dedicated unit to provide primary air (mainly
> ventilation air) to the beams at 55 degrees. I’ve modeled the chilled beam
> system as a fan coil system, but am wondering about my options for modeling
> the primary air.
>
>
>
> My question is this: If I attach the primary/ventilation air unit to the
> fan coil system in the FC’s Outdoor Air tab under “Outside Air from System”
> will the temperature of the air coming from that unit have an impact on the
> load in the space? I have a ton of hours at very low load during the winter
> months, and I want eQuest to use the 55 degree primary air as the first
> stage of cooling for the space and not “double up” the cooling energy by
> cooling the 55 degree air and then not use that for cooling in the zones.
>
>
>
> If anybody has some input, it would be appreciated.
>
>
>
> *Greg Collins*
> Design Engineer / Energy Analyst
>
> Mechanical Department
> LEED® Accredited Professional
>
> [image: http://www.glumac.com/glumacsig.gif] <http://www.glumac.com/>
> ------------------------------
>
> NOTE OUR NEW ADDRESS
>
> 18200 Von Karman Ave., Suite 100
> Irvine, CA 92612
> T. 949.833.8190 F. 949.833.0252
>
> *Thinking. Inside the building.*
> www.glumac.com
>
>
> ------------------------------
>
> The information contained in this communication is confidential, may be
> privileged, and is intended only for the use of the addressee. It is the
> property of GHT Limited. Unauthorized use, disclosure or copying of this
> communication or any part thereof is strictly prohibited and may be
> unlawful. If you have received this communication in error, please notify
> me immediately by return e-mail or by e-mail to ght at ghtltd.com, and
> destroy this communication and all copies thereof, including all
> attachments. Thank you.
>
>
>
>
>
> _______________________________________________
>
> Equest-users mailing list
>
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if any)
> are intended solely for the use of the addressees hereof. In addition, this
> message and the attachments (if any) may contain information that is
> confidential, privileged and exempt from disclosure under applicable law. If
> you are not the intended recipient of this message, you are prohibited from
> reading, disclosing, reproducing, distributing, disseminating or otherwise
> using this transmission. Delivery of this message to any person other than
> the intended recipient is not intended to waive any right or privilege. If
> you have received this message in error, please promptly notify the sender
> by reply E-mail and immediately delete this message from your system.
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100409/c741a329/attachment.htm>
More information about the Equest-users
mailing list