[Equest-users] Active Chilled Beam/Fan Coil System
Greg Collins
GCollins at glumac.com
Fri Apr 9 13:32:18 PDT 2010
I have tried it, but I end up getting an error saying the leaving air
temp off the coil needs to be at least 6F higher than the entering water
temp to the coil, and for some reason I don't get the same error for the
FCU. In an active chilled beam, the coil is actually just cooling the
room induction air, then mixing it with the primary air from the DOAS.
I think that equest assumes the air mixes before entering the coil,
which fundamentally is the same thing, but the numbers trip this error
message. I'll look into more why the FC system doesn't make that
happen, but the two seem to be essentially the same system except for
the fan (which I make 0.000001 kW/cfm anyway).
From: Grando, John [mailto:JGrando at cosentini.com]
Sent: Friday, April 09, 2010 1:00 PM
To: Greg Collins; Bruce Easterbrook
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Active Chilled Beam/Fan Coil System
Have you looked into SYSTEM TYPE = IU (Induction Unit). This may be a
better path to try.
John Grando LEED AP| Mechanical Engineer
________________________________
From: Greg Collins [mailto:GCollins at glumac.com]
Sent: Friday, April 09, 2010 2:00 PM
To: Bruce Easterbrook
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Active Chilled Beam/Fan Coil System
Bruce,
I agree with your theory and the justification, but the question is
ultimately "how to model it?" I don't think you can put in negative
heat for a baseboard system, hook it up to a chilled water loop and get
results you can count on.
Greg
From: Bruce Easterbrook [mailto:bruce5 at bellnet.ca]
Sent: Friday, April 09, 2010 8:59 AM
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Active Chilled Beam/Fan Coil System
I'm not totally up on using DOAS with eQuest or with chilled beams
being in Canada but it would seem to me the OA will have to be used to
control humidity in the space. The chilled beam should not be used for
latent cooling, sensible only, to prevent condensation issues. The DOAS
will need to control the dewpoint of the room air and maintain it below
the operating temperature of the coil in the chilled beam. The chilled
beam would only be dealing with the sensible load from the space. The
DOAS would do everything else. The question would be will eQuest allow
a single zone AHU c/w economizer and a baseboard system with negative
heat? I have never tried that with eQuest.
Bruce Easterbrook
Abode Engineering
On 08/04/2010 04:46 PM, James Hansen wrote:
I'm interested in this as well - I know that in DOAS systems like active
chilled beams, the primary air often takes on a fairly large chunk of
space latent cooling, and if this can't be passed on from the DOAS
system to the space, then I don't see how we can believe the results.
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Greg
Collins
Sent: Thursday, April 08, 2010 4:39 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Active Chilled Beam/Fan Coil System
Hi all,
I'm working on modeling an active chilled beam system. It consists of
the chilled beams and a dedicated unit to provide primary air (mainly
ventilation air) to the beams at 55 degrees. I've modeled the chilled
beam system as a fan coil system, but am wondering about my options for
modeling the primary air.
My question is this: If I attach the primary/ventilation air unit to
the fan coil system in the FC's Outdoor Air tab under "Outside Air from
System" will the temperature of the air coming from that unit have an
impact on the load in the space? I have a ton of hours at very low load
during the winter months, and I want eQuest to use the 55 degree primary
air as the first stage of cooling for the space and not "double up" the
cooling energy by cooling the 55 degree air and then not use that for
cooling in the zones.
If anybody has some input, it would be appreciated.
Greg Collins
Design Engineer / Energy Analyst
Mechanical Department
LEED(r) Accredited Professional
<http://www.glumac.com/>
________________________________
NOTE OUR NEW ADDRESS
18200 Von Karman Ave., Suite 100
Irvine, CA 92612
T. 949.833.8190 F. 949.833.0252
Thinking. Inside the building.
www.glumac.com <http://www.glumac.com/>
________________________________
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is
the property of GHT Limited. Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful. If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments. Thank you.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if
any) are intended solely for the use of the addressees hereof. In
addition, this message and the attachments (if any) may contain
information that is confidential, privileged and exempt from disclosure
under applicable law. If you are not the intended recipient of this
message, you are prohibited from reading, disclosing, reproducing,
distributing, disseminating or otherwise using this transmission.
Delivery of this message to any person other than the intended recipient
is not intended to waive any right or privilege. If you have received
this message in error, please promptly notify the sender by reply E-mail
and immediately delete this message from your system.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100409/cc54ee8d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 6582 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100409/cc54ee8d/attachment.gif>
More information about the Equest-users
mailing list