Nick Caton ncaton at smithboucher.com
Fri Apr 9 08:44:35 PDT 2010


Food for thought - I really enjoy hearing how others would approach things...  My intuitive approach would also involve detailed work but perhaps less so (?), and without any *.inp work... 

 

Alternate Option 3)  Combine shells 2 + 3 at the wizard level (and if reasonable/feasible, floors below as a 2 or 3 story shell), defining the roof construction that will be exposed in the wizards (as a custom construction if possible).  In detailed mode 2D or 3D view, scroll through the Shell 2+3 spaces, and simply right-click à Delete... any roof polygons occurring immediately below shell #1.  This will eliminate any gains/losses to those zones from Shell #1 above.

 

For any of these approaches, make sure for Shell #1 you select "Over Conditioned Space (adiabatic)" for the floor construction.

 

Running note - as a caution, there are reasons NOT to make 2/3 story shells in the wizards based on my recent experience.  Daylighting controls may turn out to be un-defineable (in the wizards) for middle/ground floors if that's a concern.

 

~Nick

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Friday, April 09, 2010 10:00 AM
To: Richard Williams; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Shell stacking options

 

Richard,

 

I usually use option 3 - create one shell per floor and add roofs as necessary wherever the lower floors are exposed. (So create your shell 2/3 as one shell and create a roof(s) above the zones in shell 3.) This requires copying/modifying polygons, which I find easier to do within the input files. After you do it a couple times it's not so bad.

 

Regards,

Bill

 

William Bishop, EIT, BEMP, LEED® AP | Pathfinder Engineers & Architects LLP

Mechanical Engineer

 

134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005

wbishop at pathfinder-ea.com

www.pathfinder-ea.com

P Please strive to live sustainably.

________________________________

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Richard Williams
Sent: Friday, April 09, 2010 10:46 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Shell stacking options

 

Hi again

 

A while ago I posted a question about the use of shells and receive some very useful responses explaining that best practice is to use different shells for each exposure/adjacency combination. I have a follow up question to this which is a little tricky to explain but hopefully the attached will help.

 

The attached shows two shell variants for the same building. The top floor (shell 1) is smaller than the other floors. Therefore, for both variants the floor below is broken into two shells; shell 2 which is exposed to the top floor and shell 3 that has a roof exposed to atmosphere. My question relates to the floor below these. Can this be comprised of a single shell which spans both shell 2 and 3 as per option 1, or does it need to be broken into two to match the shells above as per option 2?

 

Regards

 

Richard

 

 

 

Ps thanks to Nick for pointing me in the direction of last week's discussion on shading geometry

 

 

 

From: Richard Williams 
Sent: 09 April 2010 11:03
To: 'equest-users at lists.onebuilding.org'
Subject: Non-rectangular building shade

 

Hello

 

Is it possible to use non-rectangular polygons as shade? If so how do I do this?

 

Any suggestions much appreciated.

 

Regards

 

Richard

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100409/e1cfd7d4/attachment.htm>