[Equest-users] Actual Weather Data
Thomas Serra
tserra at emoenergy.com
Fri Apr 2 10:24:34 PDT 2010
I have had success purchasing weather data from Weatherbank. After hours of
trying to figure out how to use the "free" data I was confronted with
client requirements that the filled data be supported with proper PHD skill.
So to satisfy this requirement I purchased the file. I would suggest
getting several years and several stations as the price scales down with
quantity.
You can then use a combination of the Energyplus weather tool and equest
doe2 weather tools to build TMY2 files. Find a epw file for your climate
and use the energy plus weather tool to convert to CSV. Convert units and
paste into the CSV. Use the EP weather tool to convert back to EPW. Then
convert the EPW with the EQ weather tool to TMY2.
Thomas Serra
Project Manager
EMO Energy Solutions, LLC
3141 Fairview Park Drive, Suite 450
Falls Church, VA 22042
voice 703-205-0445 ex-113
fax 703-205-0449
From: Keith Curtis [mailto:kcurtis at emcengineers.com]
Sent: Monday, March 22, 2010 3:47 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Actual Weather Data
Hello Gang,
I'm trying to develop an Equest model with actual weather data for 2008 for
Atlanta, Georgia.
I can get the TMY (or TM2, TM3) data and convert it to a CSV file and copy
(or convert) all the weather data and then convert back to a *.bin file.
BUT, I CAN'T find hourly Solar Global Horizontal or Solar Direct Normal
Irradiance data for Atlanta.
Anybody ever do this or know where to find the solar data? Thanks in
advance.
Keith Curtis
Senior Mechanical Engineer
kcurtis at emcengineers.com
678-254-1200 - Office
678-254-1228 - Direct
678-254-1239 - Fax
EMC Logo-JPEG 070823.jpg
http://www.emcengineers.com/
Making buildings work. Better. Since 1976
Confidentiality Notice: This message and any materials attached are
confidential, and are intended solely for the use of the addressee. If you
are not the intended recipient, be advised that unauthorized use,
disclosure, copying, or distribution is strictly prohibited. If you
received this message in error, please notify the sender and destroy your
copy immediately.
P Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100402/d18fe2b4/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2573 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100402/d18fe2b4/attachment.jpeg>
More information about the Equest-users
mailing list