[Equest-users] SUPPLY-KW/FLOW - question answered
Lars Fetzek
lfetzek at phoenixeng.us
Thu Sep 17 12:12:41 PDT 2009
Thanks, everybody, for the many replies to this question. It has been
answered.
_____
From: Lars Fetzek [mailto:lfetzek at phoenixeng.us]
Sent: Wednesday, September 16, 2009 4:59 PM
To: 'Lars Fetzek'; 'equest-users at lists.onebuilding.org'
Subject: RE: [Equest-users] SUPPLY-KW/FLOW
Question answered. Thanks, everyone.
Lars Fetzek, EI
Phoenix Engineering Group
Tampa, Florida
_____
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Lars Fetzek
Sent: Wednesday, September 16, 2009 4:48 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] SUPPLY-KW/FLOW
eQuesters & DOE2-2ers,
The DOE2-2 dictionary loves to use the phrase, "total fan power per unit
flow" in defining SUPPLY-KW/FLOW. Clear as mud.
I figured this: At design conditions, the supply fan runs at 9.90 BHP
and 61.89% efficiency and the per-unit flow is at unity ( x CFM / x CFM =
1). The motor nominal efficiency is 93%. (No, I don't have a motor
efficiency curve.) 0.746 kW = 1 HP. Therefore, the fan kW = 9.90 *
0.746 / ( 0.6189 * 0.93 ) = 12.83 kW. The per unit flow is 1. So...
SUPPLY-KW/FLOW = 12.83, which I type into my .inp file.
Naturally, eQuest gives me an error message, insisting that
SUPPLY-KW/FLOW must be between 0.0 and .0080. Evidently, there is some
discrepancy involving units or the meaning of "per unit" in the context of
the quoted phrase.
Can anyone clarify what eQuest really means and how to calculate
SUPPLY-KW/FLOW? Is it supposed to be KW-per-CFM?
Thanks!
Lars Fetzek, EI
Phoenix Engineering Group
Tampa, Florida
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090917/dd1dd613/attachment.htm>
More information about the Equest-users
mailing list