[Equest-users] Adjacent Shells
Dakota Kelley
dakotak at teliospc.com
Thu Nov 12 11:57:35 PST 2009
Sheri,
After reading the subtext of this message chain, what I think you’re trying to accomplish is not possible in the wizard (multiple exterior wall constructions with inter-zone heat transfer). I’m sure this undermines all the work you’ve done thus far, but you’ll save quite a bit of time and have a much better project by adjusting the exterior wall constructions in the detailed interface rather than creating a new shell for each construction. Let me explain and comment on the message history:
· eQUEST will create adiabatic interior walls between two adjacent shells if the shell coordinates line up along a common plane. Therefore, if the end goal of creating multiple shells is to account for inter-shell heat transfer and have multiple exterior wall constructions, some use of the detailed interface is required. You will have to adjust either the interior walls (from adiabatic to standard) or the exterior wall constructions in the detailed interface. It is by far faster to adjust the exterior wall constructions. If you opt to change the interior walls from adiabatic to standard, you’ll be prompted for the adjacent zone for each wall. If you have three shells per floor, it sounds like you’ll need to create a spreadsheet or rename all zones in all shells to something more identifiable than “EL1 East Perim Zn (G.E2)”.
· In the wizard, when a zone is created that is partially exterior and partially adjacent to another shell, the walls along the plane of intersection will be broken up between interior and exterior walls according to what’s on the other side. Where the two zones in separate shells touch, each zone will be assigned an adiabatic interior wall as mentioned above.
· Per Jim’s example below, for any wall that is drawn in the wizard but does not touch the building footprint or another zone, an adiabatic interior wall will be assigned. The wall is basically there to soothe the user – eQUEST couldn’t care less if the wall is adiabatic or not there at all.
· By definition, an interior wall (adiabatic or standard) will never communicate thermally with the exterior. For what Nick described below to occur, one would have to use the detailed interface to manually assign an interior wall construction to a wall that is defined as exterior. The conversation has mixed the concepts of wall type and construction – these are separate properties. Wall type dictates where heat is transferred, construction simply dictates the rate and delay (thermal massing).
· Also by definition, an exterior wall will never communicate thermally between two zones; it can only transfer thermal energy between its parent zone and the exterior
· I used the tons-of-shells approach on my first project and ended up with over 10 shells. eQUEST would crash when I tried to run the simulation. What I didn’t quite realize is that when you create a new shell, eQUEST is going to create new occupancy, lighting, equipment, etc., schedules as well as new constructions for all interior and exterior surfaces. True, each shell’s schedules and constructions could have the same properties, but they are still viewed as separate entities and add a lot of weight to your project file. At four or five shells users will see a noticeable delay in opening, saving, and simulating files. Done to extreme, the project becomes too cumbersome to simulate.
· One can be assured that time, complication, and frustration will be added to any project by trying to do it all in the wizard.
With regard to what you’ve witnessed thus far, I would bet that there’s a conflict between the coordinates/reference location a shell is given on Wizard Screen 1 and where that shell is actually drawn on Screen 2 (assuming you’re tracing a CAD file). Where it did create an internal wall, the common plane between Screen 1 and 2 jived. That’s about as accurately as I can describe it in an email. Try creating two adjacent shells in a test file using only site coordinates and aspect ratios and you’ll see what I mean after inspecting the shells in the detailed interface.
To bring this full-circle, it will be faster and more accurate to create as few shells as possible in the wizard and then use the detailed interface to create/assign additional wall constructions. The most prevalent wall construction should be specified in the wizard to reduce the number of changes in the detailed interface.
Regards,
DAKOTA KELLEY
Project Designer
Office: 214-744-6199
Cell: 214-280-3825
Fax: 214-744-0770
http://www.teliospc.com <http://www.teliospc.com/> 3535 Travis St. Suite 115
dakotak at teliospc.com <mailto:dakotak at teliospc.com> Dallas, TX 75204
| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed,
And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you
are not the intended recipient, please email the sender immediately, and delete this email from all computers. Any
distribution or other use is strictly prohibited. Copyright © 2009 Telios Corporation.
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Wednesday, November 11, 2009 2:26 PM
To: Crockett, Jim; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Adjacent Shells
Jim,
I think the issue-at-hand here, if I’m understanding correctly, is that there’s concern an internal wall created by avoiding the footprint perimeter will simply use the defined internal wall construction and transfer to/from the outside… I’m not certain (and I haven’t tested this) that you want to answer “don’t care” without verifying this isn’t the modeled behavior.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Crockett, Jim
Sent: Wednesday, November 11, 2009 1:15 PM
To: John Aulbach; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Adjacent Shells
Not sure. But if the set point on both sides of the wall is the same, the heat transfer will be negligible. Short answer is ‘don’t care.’
________________________________
From: John Aulbach [mailto:jra_sac at yahoo.com]
Sent: Wednesday, November 11, 2009 12:13 PM
To: Crockett, Jim; Rocha, Sheri; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Adjacent Shells
Jim:
Will you get the internal heat ransfer between these walls? Or will you care?
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
Partner Energy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com <http://www.ptrenergy.com/> | jaulbach at ptrenergy.com <mailto:%7C%20jaulbach at ptrenergy.com>
________________________________
From: "Crockett, Jim" <Jcrockett at nexant.com>
To: "Rocha, Sheri" <srocha at mkkeng.com>; equest-users at lists.onebuilding.org
Sent: Wed, November 11, 2009 9:28:33 AM
Subject: Re: [Equest-users] Adjacent Shells
We accidentally stumbled onto a way of doing this.
If the walls on the zoning tab do not line up with the walls on the shell tab, they will show up as internal walls.
Example 1
Shell:
(0,0) (100,0) (100,100) (0,100)
Zone:
(1,1) (99,1) (99,99) (1,99)
This will create a zone surrounded by 4 internal walls.
Example 2
Shell:
(0,0) (100,0) (100,100) (0,100)
Zone:
(1,0) (99,0) (99,99) (1,99)
Will create a zone with 1 external wall ( on the south side) and 3 internal walls.
Hope this helps.
Jim
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rocha, Sheri
Sent: Wednesday, November 11, 2009 9:45 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Adjacent Shells
I am modeling a building with multiple wall types therefore I have 3 shells per floor. I am trying to figure out how to have the adjacent walls between shells be modeled as interior instead of exterior. In one of spot they came out as interior, but I am not sure how I did it. I am trying to do as much in the wizard as possible. Does anyone know how to do this??
Thanks for your help.
Sheri Rocha, P.E. , LEEDTM AP
Senior Mechanical Engineer
srocha at mkkeng.com <mailto:srocha at mkkeng.com>
www.mkkeng.com <http://www.mkkeng.com/>
P Save a Tree. Don't print this e-mail unless necessary.
7600 E. Orchard Road
Suite 250-S
Greenwood Village, CO. 80111
Direct: 303-796-6062
Main: 303-796-6000
Fax: 303-796-6099
CONFIDENTIALITY NOTICE: This e-mail and any attached file(s) are intended only for the use of the individual or entity to whom or to which it is addressed and may contain information that is privileged, confidential, proprietary, and trade secret. If the reader of this message is not the intended recipient or an employee or agent responsible for delivering the message to the intended recipient, you are hereby notified that any dissemination, distribution, or reproduction of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately and discard the original message and any attachment(s).
__________________________________________________
Do You Yahoo!?
Tired of spam? Yahoo! Mail has the best spam protection around
http://mail.yahoo.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091112/3942ad8c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091112/3942ad8c/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3209 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091112/3942ad8c/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3170 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091112/3942ad8c/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2327 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091112/3942ad8c/attachment-0002.jpeg>
More information about the Equest-users
mailing list