[Equest-users] R-Value problem
    Pasha Korber-Gonzalez 
    pasha.pkconsulting at gmail.com
       
    Fri Nov  6 12:00:01 PST 2009
    
    
  
Martin,
when you are in the wizard, it is actually asking you to build-up your wall
construction for eQuest to calculate the overall Assembly u-value which
includes the thermal effects of the exterior surface/cladding + the
insulation + the frame conductance (for frame walls, etc.)  The R-value to
which you refer is specific only to the thermal properties of the
insulation--nothing else in the assembly.
when you are in DDedit mode in the spreadsheet the input approch is
different and more flexible.  In this mode you can build-up your
constructions based on the types of layers in the construction from the
outside to inside surfaces.  OR, under the column labled "specification
method" you can use the drop down box to select either 'layers' or
'u-value'.  When you select u-value with this approach this is the input
U-value for the overall assembly construction, not just the u-value for the
insulation.  The u-value approach is the simplified, quick way, but when you
have requirements as in ASHRAE 90.1 Appedix G, you have to use the layers
method.  If you do use the u-value in DDedit mode, make sure you know what
your overall assembly u-value will be.  The insulation R-value will always
be higher than your overall construction assembly R-value (u-value
equivalent), becuse of the additional thermal losses conducted through the
other surfaces--especially dramatic when you evaluate a steel-frame
construction.  There is a software program that will calculate the overal
construction thermal performance as a built up building (outside of
eQuest.)  I think this program is called Therm, but not sure.
Pasha
On Fri, Nov 6, 2009 at 12:36 PM, Martin Ménard <marmenard at gmail.com> wrote:
> Hi all eQUEST user!
> I'm a bit confused about my input values inside the Wizard mode VS Detail
> mode.
> In "Building Envelope Constructions" window (3 of 25) I put an Overall
> R-Value of 20 h-ft2-°F/Btu...
> But, when I go into the spreadsheet view (in Detail mode) and take a look
> at the Constructions details, I see a U Value of 20 Btu/h-ft2-°F!?
> It's not realy the same thing!
>
> Did you know why the software does not make the convertion R to U value
> correctly? Or is it my mistake? Should I put a U value when the software
> asks me to put an R value in the Wizard window?
>
> Thanks to all and sorry for my poor English (it's not my first language) !
> :-)
>
> Martin
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091106/73737f67/attachment.htm>
    
    
More information about the Equest-users
mailing list