<div>when you are in the wizard, it is actually asking you to build-up your wall construction for eQuest to calculate the overall Assembly u-value which includes the thermal effects of the exterior surface/cladding + the insulation + the frame conductance (for frame walls, etc.)  The R-value to which you refer is specific only to the thermal properties of the insulation--nothing else in the assembly.</div>

<div> </div>
<div>when you are in DDedit mode in the spreadsheet the input approch is different and more flexible.  In this mode you can build-up your constructions based on the types of layers in the construction from the outside to inside surfaces.  OR, under the column labled "specification method" you can use the drop down box to select either 'layers' or 'u-value'.  When you select u-value with this approach this is the input U-value for the overall assembly construction, not just the u-value for the insulation.  The u-value approach is the simplified, quick way, but when you have requirements as in ASHRAE 90.1 Appedix G, you have to use the layers method.  If you do use the u-value in DDedit mode, make sure you know what your overall assembly u-value will be.  The insulation R-value will always be higher than your overall construction assembly R-value (u-value equivalent), becuse of the additional thermal losses conducted through the other surfaces--especially dramatic when you evaluate a steel-frame construction.  There is a software program that will calculate the overal construction thermal performance as a built up building (outside of eQuest.)  I think this program is called Therm, but not sure.</div>

<div> </div>
<div>Pasha<br><br></div>
<div class="gmail_quote">On Fri, Nov 6, 2009 at 12:36 PM, Martin Ménard <span dir="ltr"><<a href="mailto:marmenard@gmail.com">marmenard@gmail.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Hi all eQUEST user!<br>I'm a bit confused about my input values inside the Wizard mode VS Detail mode.<br>
In "Building Envelope Constructions" window (3 of 25) I put an Overall R-Value of 20 h-ft2-°F/Btu...<br>But, when I go into the spreadsheet view (in Detail mode) and take a look at the Constructions details, I see a U Value of 20 Btu/h-ft2-°F!?<br>
It's not realy the same thing!<br><br>Did you know why the software does not make the convertion R to U value correctly? Or is it my mistake? Should I put a U value when the software asks me to put an R value in the Wizard window?<br>
<br>Thanks to all and sorry for my poor English (it's not my first language) ! :-)<br><font color="#888888"><br>Martin<br></font><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>