Kimberly,

You need to make changes in the .inp file, not the bdl file.  Cut the dummy MAU system in the .inp file and paste it before the Fan Coil System.

Good luck,


Jon Evans, PE, LEED AP



Sustainable Engineering Group LLC

431 Charmany Drive Suite 102

Madison, WI 53719



Tel: (608) 231 9664 x 13

Fax: (608) 231 9665

E-mail: jevans at sustaineng.com

Web: www.sustaineng.com

________________________________
From: Kimberly Killian [mailto:kimberly at northernarchitects.com]
Sent: Wednesday, June 17, 2009 8:29 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] (no subject)

Good afternoon,

I am trying to add a mixed air unit onto a four-pipe fan coil system through the use of a dummy zone, from which my real zones will get their outside air. I get the following error:

"EL1 Sys1 (FC) (G.E16) defined before its OA-FROM-SYSTEM. This will cause incorrect OA temperature calculation. Move this SYSTEM to be defined before its OA-FROM-SYSTEM in the project BDL input file."

The catch is that there is no BDL file, as the simulation aborts before it is complete. Is there another way to define the MAU before the Fan Coil System. I have searched a number of terms in the user's group and there are many questions related to this topic, but I can't find any answers. Any help would be appreciated.

Regards,
Kimberly Killian
Northern Architects, Inc.
207 King Street Suite 3
Burlington VT 05401
T: 802-658-1953
F: 802-658-2975
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090617/cda7e7d4/attachment.htm>


More information about the Equest-users mailing list