[Equest-users] Difference in results for different eQuest	versions v3.61 and v3.63 for same model...
    Kendra Tupper 
    ktupper at rmi.org
       
    Thu Jul  9 08:54:46 PDT 2009
    
    
  
This is from the bug that was discovered earlier - the fix is to overwrite
the eQUEST default for min cfm ratio (heating). Here is the code that should
be used:
if (#P("HMIN-CFM-RATIO") == unused)
    then unused
    else if (#RV(#P("HMIN-CFM-RATIO")) == 0)
          then #P("HMIN-CFM-RATIO")
          else no_default
         endif
   endif
Kendra Tupper, PE, LEED AP
Senior Consultant
Built Environment Team
Rocky Mountain Institute  |  T  303-567-8641 |  F  303-245-7213  |
www.rmi.org
On Thu, Jul 9, 2009 at 1:02 AM, Pawan Mulchandani <pawan.equest at gmail.com>wrote:
> Hi all,
>
> I tried to compare results from two different eQuest versions i.e. 3.61b
> and 3.63 with a same model with default eQuest settings. But I found there
> is large difference in space cooling and vent fans load in both the version
> results even though the models are same. Space cooling for v3.61 is 85.02 X
> 1000 kWh alongwith vent fans load of 36.14 X 1000 kWh. While for v3.63 space
> cooling is 6.87 X 1000 kWh and vent fans load is 66.01 kWh. I cant
> understand why there is such a large difference in the output. Is there any
> large difference in the algorithms in both the versions?? Please find
> attached .inp files for both the versions and also the weather file for
> mumbai. Please go through the files..
>
> Thanks & Regards,
> Pawan.M.
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090709/07826d22/attachment.htm>
    
    
More information about the Equest-users
mailing list