This is from the bug that was discovered earlier - the fix is to overwrite the eQUEST default for min cfm ratio (heating). Here is the code that should be used:<br><br>if (#P("HMIN-CFM-RATIO") == unused)<br> then unused<br>
else if (#RV(#P("HMIN-CFM-RATIO")) == 0)<br> then #P("HMIN-CFM-RATIO")<br> else no_default<br> endif<br>
endif <br><br><br clear="all">Kendra Tupper, PE, LEED AP<br>Senior Consultant<br>Built Environment Team<br><br>Rocky Mountain Institute | T 303-567-8641 | F 303-245-7213 | <a href="http://www.rmi.org">www.rmi.org</a><br>
<br><br><div class="gmail_quote">On Thu, Jul 9, 2009 at 1:02 AM, Pawan Mulchandani <span dir="ltr"><<a href="mailto:pawan.equest@gmail.com">pawan.equest@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
Hi all,<br><br>I tried to compare results from two different eQuest versions i.e. 3.61b and 3.63 with a same model with default eQuest settings. But I found there is large difference in space cooling and vent fans load in both the version results even though the models are same. Space cooling for v3.61 is 85.02 X 1000 kWh alongwith vent fans load of 36.14 X 1000 kWh. While for v3.63 space cooling is 6.87 X 1000 kWh and vent fans load is 66.01 kWh. I cant understand why there is such a large difference in the output. Is there any large difference in the algorithms in both the versions?? Please find attached .inp files for both the versions and also the weather file for mumbai. Please go through the files..<br>
<br>Thanks & Regards, <br>Pawan.M.<br>