Brett,
It also looks like you are specifying zone-level exhaust flows. When summing the maximum zone values of OA cfm or exhaust cfm, you get 4642 cfm, which is the OSA cfm reported for your baseline building. You probably have the OA-SIZING-METHOD set to the default "SUM-OF-ZONE-OA" for the baseline and "SET-BY-CRITICAL-ZONE" for the proposed.
Bill
William Bishop, EIT, LEED® AP | Pathfinder Engineers LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
bbishop at pathfinderengineers.com
 
www.pathfinderengineers.com
P Please strive to live sustainably.
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Min-Hwan Yang
Sent: Thursday, August 27, 2009 10:18 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Zone report OA discrepancy
Brett,
It looks like your critical zone caused that.  It seems you have reduced cooling CFM by trying to reduce cooling load at exterior zones. 
By reducing cooling CFM the program bumped OSA ratio to meet the zone OA requirement.  I would suggest you should increase the min. CFM of box serving the critical zone (G.SSW4).
Thanks,
Min-Hwan Yang, CEM, LEED AP
Mechanical Engineer | yangm at kjww.com
200 West Jackson Boulevard, Suite 1200 | Chicago, Illinois 60606
312-294-0501 | Direct: 312-356-3750 | Fax: 312-294-0003
www.kjww.com
When looking at my Zone Air-Side Summary Report I noticed that the proposed system OSA cfm was about double that of my baseline building. However, all the zone OSA quantities are equal. Does anyone know what could cause this discrepancy? I have attached pdf files for both the proposed and baseline report. Thanks in advance.
Brett M. West
Design Engineer-Mechanical
 
RMF Engineering, Inc.
T: 843-971-9639 ext. 1499
F: 843-971-9641
bwest at rmf.com
This message and any attachments contain information intended for a specific party and may include sensitive or confidential material. If you are not the intended recipient, please do not read, copy, use, or disclose to others.  Please notify the sender of the delivery error by reply and then permanently delete this message and all attachments.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
    
    
More information about the Equest-users
mailing list