[Equest-users] Zone report OA discrepancy
Min-Hwan Yang
yangm at kjww.com
Thu Aug 27 07:18:14 PDT 2009
Brett,
It looks like your critical zone caused that. It seems you have reduced cooling CFM by trying to reduce cooling load at exterior zones.
By reducing cooling CFM the program bumped OSA ratio to meet the zone OA requirement. I would suggest you should increase the min. CFM of box serving the critical zone (G.SSW4).
Thanks,
Min-Hwan Yang, CEM, LEED AP
Mechanical Engineer | yangm at kjww.com
200 West Jackson Boulevard, Suite 1200 | Chicago, Illinois 60606
312-294-0501 | Direct: 312-356-3750 | Fax: 312-294-0003
www.kjww.com
When looking at my Zone Air-Side Summary Report I noticed that the proposed system OSA cfm was about double that of my baseline building. However, all the zone OSA quantities are equal. Does anyone know what could cause this discrepancy? I have attached pdf files for both the proposed and baseline report. Thanks in advance.
Brett M. West
Design Engineer-Mechanical
RMF Engineering, Inc.
T: 843-971-9639 ext. 1499
F: 843-971-9641
bwest at rmf.com
This message and any attachments contain information intended for a specific party and may include sensitive or confidential material. If you are not the intended recipient, please do not read, copy, use, or disclose to others. Please notify the sender of the delivery error by reply and then permanently delete this message and all attachments.