[Equest-users] System per Area for Packaged VAV with Elec Reheat
Kosuke
kosuke at cmtaegrs.com
Thu Aug 6 12:35:39 PDT 2009
Rick,
According to ASHRAE 90.1 addendum u, a base model needs to be served by
" system per floor" for system 5, 6, 7, 8. Your packaged VAV with elec.
reheat will be fall under this category. Also your thermal zone must by
as same as in proposed model.
Kosuke Kato, LEED AP
Senior Energy Modeling Engineer
CMTA Consulting Engineers, Inc.
Louisville - Lexington KY
Lou. 502 326 3085
Lex. 859 253 0892
kosuke at cmtaegrs.com <mailto:kosuke at cmtaegrs.com>