[Equest-users] System per Area for Packaged VAV with Elec Reheat

ashu gupta kce2 at kamalcogentenergy.com
Thu Aug 6 04:48:20 PDT 2009


Rick,

 

Do default on static pressure box then the kw/CFM box can activate.

 

Thanks

Ashu

 





  _____  

From: YinRic [mailto:cesseric at hotmail.com] 
Sent: Thursday, August 06, 2009 1:22 PM
To: kce2 at kamalcogentenergy.com; Equest User
Subject: RE: [Equest-users] System per Area for Packaged VAV with Elec Reheat

 

Hi Ashu,
 
When I attempt to enter kw/cfm, the space is in grey with "n/a". Can you advise how I can activate the blank and fill in the number?
 
Many thanks,
Rick
 

  _____  

From: kce2 at kamalcogentenergy.com
To: cesseric at hotmail.com
Subject: RE: [Equest-users] System per Area for Packaged VAV with Elec Reheat
Date: Thu, 6 Aug 2009 12:24:38 +0530

Hi Rick,

 

You must entered the Fan power as kw/cfm in every system in baseline system

 

Thanks

Ashu

 

  _____  

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of YinRic
Sent: Thursday, August 06, 2009 12:01 PM
To: Equest User
Subject: [Equest-users] System per Area for Packaged VAV with Elec Reheat

 

Hi All,
 
We have a 4-story office building to be LEED certified. The Baseline system is packaged VAV with elec reheat. After reviewed by GBCI, the comment is:
 
"The Baseline case fan power does not appear to be modeled in accordance with G3.1.2.9. Please revise the sum of the supply, return, exhaust and relief fans for each HVAC system to be equal to the power calculated in G3.1.2.9."
 
Now I am ready to revise the model, but I am not sure in the baseline case, whether I must choose "system per shell", "system per floor" or "system per zone". Could anyone advise? Thanks in advance. 
 
Rick, PE, LEED AP

  _____  

聊天+搜索+邮箱 想要轻松出游,手机MSN帮你搞定!  <http://mobile.msn.com.cn/> 立刻下载!

 

  _____  

搜索本应是快乐的,不是么? 快乐搜索,有问必应!微软隆重推出!  <http://bing.com.cn?FORM=M00HCN&Publ=WLHMTAG&Crea=TEXT_Search_Where_You_Are_1X1> 立即试用!

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090806/1dc246fb/attachment.htm>


More information about the Equest-users mailing list