[Equest-users] Chiller Type

B. Fountain bfountain at greensim.com
Wed Aug 5 09:09:51 PDT 2009


One possible solution would be to define both refrigeration plants in the
baseline model and then create two Equipment Controls -- one for the
proposed building with only the single centrifugal chiller enabled and one
for the ASHRAE reference with the 2 screw chillers enabled (without the
centrifugal).  In the parametric run for the chilled water loop you can
change the Cool Equipment Control selection under loop control.

Check the PS-H report for all chillers to see that the strategy worked.


> Hi,
> I'm modeling a high rise residential building. The proposed building has
> one centrifugal chiller but based on ASHRAE, the reference building should
> have two rotary screw chillers, but eQuest doesn't allow me to have
> different type of chillers in parametric run. In parametric run when I try
> to change the type of the chiller, the program crashes. Any comment?
>
> Thanks in advance.
>
> Hassan Zareh, M.Eng., P.Eng., LEED® AP
> Project Engineer
> Stantec Consulting Ltd.
> 100 - 401 Wellington Street West
> Toronto ON M5V 1E7
> Ph: (416) 598-7642
> Fx: (416) 596-6680
> hzareh at stantec.com
> stantec.com <http://www.stantec.com/>
>
> The content of this email is the confidential property of Stantec and
> should not be copied, modified, retransmitted, or used for any purpose
> except with Stantec's written authorization. If you are not the intended
> recipient, please delete all copies and notify us immediately.
>
> ü Please consider the environment before printing this email.
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>





More information about the Equest-users mailing list