1)            The easiest way to create a building with multiple shells
to turn on "specify exact site coordinates" under general shall
information on DD wizard.  Keep X and Y coordinate to 0,0.  If you want
to create a shall above another shell, just change z coordinates.
2)            Your initial model is baseline model.  If you go to energy
efficiency measure (EEM)  wizard, you can run same energy model with
different HVAC efficiency, building R-value, and etc.  This time, EEM
run name will be shown on the simulation reports with your baseline
model.
3)            If you want to compare the results to ASHRAE 90.1, you
have to insert all the Appendix G requirement by hand.
 
 