[BLDG-SIM] glass u-vals
Leonard Sciarra
leonard_sciarra at gensler.com
Wed Apr 18 07:07:23 PDT 2007
also see the envelope section of the 90.1 users manual, there they talk
about the difference between center of glass and frame, etc...
Leonard Sciarra, AIA, LEED ap
312.577.6580 (Dir)
G E N S L E R | Architecture & Design Worldwide
30 West Monroe Street
Chicago IL, 60603
312.456.0123
leonard_sciarra at gensler.com
________________________________
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Annalisa
Simonella
Sent: Wednesday, April 18, 2007 3:37 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] glass u-vals
Hi Aaron,
The overall U-value is usually significantly higher than the centre-pane
U-value. In order to estimate the overall U-value of curtain walls or
windows you need to include the frames U-values and the edge effects and
the additional effect of point thermal bridges if present (structural
connections through the facade or window).
You may find some guidance in the NFRC standards
http://www.nfrc.org/technicaldocs.aspx and you may use the software
THERM (downloadable from the LBNL website
http://windows.lbl.gov/software/ ) to calculate the U-value + edge
effects of frames.
You may also find some guidance in the EN ISO 10077-1 and EN ISO 10077-2
which define a different method from the NFRC one, also the first one
gives simplified method and includes a table with pre-calculated linear
thermal transmittances (edge effect).
I hope it helps.
Best regards,
Annalisa.
Annalisa Simonella
ArupFacadeEngineering
13 Fitzroy Street
London W1T 4BQ
T +44 (0)207 75 54593
F +44 (0)207 75 53626
M +44 (0)77 1781 4793
mailto:annalisa.simonella at arup.com
http://www.arup.com/facadeengineering/
________________________________
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of
Dahlstrom, Aaron
Sent: 18 April 2007 04:24
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] glass u-vals
ASHRAE 90.1 window U-vals are for the "assembly."
Manufacturer's data for my project is for "center of glass."
Is anyone familiar with a way to get from one to the other?
I have a frame type and u-value; however, Fund. Chap 31 seems to caution
against doing hand calcs due to edge-of-glass effects.
Thanks,
Aaron Dahlstrom
AKF Engineers, LLP
1500 Walnut Street, Suite 1400
Philadelphia, PA 19102
Phone: (215) 282-2169
Fax: (215) 735-6706
www.akf-engineers.com <http://www.akf-engineers.com/>
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070418/5fad07a4/attachment.htm>
More information about the Bldg-sim
mailing list