[Virtual-sim] Low DF-values with Radiance

Paul Carey paul at zed-uk.com
Tue Sep 29 01:52:29 PDT 2009


Erik/Nick

 

I’d agree on the glazing spec thing don’t go putting in very clear glass
unless you are very sure that it’s going to have those sorts of properties.
A check of the G value should help give you a guide to light transmittance.
Or just check out the Pilkington website or similar to give you a good idea,
their selection tool (think it’s called spectrum or something, a while since
I’ve used it) is quite good for getting some ideas of what it will be like.

 

In terms of the daylight studies, they should always be carried out using
the IEE overcast sky to assess daylight factors.  If you want to check out
glare etc obviously use a different sky, but for DF calculations the
overcast sky should be used.  The default positions of everything else in
IES should be ok once you’ve set that up as it will work out the working
plane levels based on that sky. 

 

Nick, you should be able to download IES for a trial from their website
normally.  Just email in a request for keys and they should set you up with
a trial.  If you haven’t checked out DesignBuilder you might want to do that
too (30 day trial available from their website).  Quite similar tool (front
end slightly more sketchup like than IES), but uses energyplus instead.
Doesn’t have the radiance link yet, but we keep pestering the guys there to
get that link in.

 

Regards

Paul

 

 

 

 

 

From: Nick Caton [mailto:ncaton at smithboucher.com] 
Sent: 28 September 2009 16:29
To: Erik Eriksson; Paul Carey
Cc: virtual-sim at lists.onebuilding.org
Subject: RE: [Virtual-sim] Low DF-values with Radiance

 

Hi Erik,

 

I’m not familiar with the limitations/capabilities of the IES Radiance tool
(still looking for a vendor in the US that can send me some kind of trial),
but I may be able to offer some suggestions based on my limited daylight
modeling experience:

 

-          To clarify, is it 12% of your wall area that is windows?

-          Again, not sure of the IES Radiance’s operation, but when you say
‘white’ floors/ceiling and ‘gray’ floors, what reflectances are being
modeled (i.e. 20/50/80%?)

-          Consider the hour/month being modeled, along with the orientation
and location on the globe.  Perhaps you’re modeling an instant in time where
there is little-to-no direct sunlight on your glazing?  

-          I am also approaching learning daylight modeling from an
energy-modeler’s perspective:  For daylight studies, I try to give myself an
idea of what should be going on first before “crunching the numbers” by
building a simple model in Google Sketchup, located/oriented on the globe,
and playing with the simplified daylighting tools to see how the sun strikes
the building through the year.  With practice I’m sure this will become more
intuitive, but until then I’ve learned not to rely on my intuitions!

-          A general heads-up that won’t solve your immediate concern:  a
visible transmittance (what IES Radiance calls “transparency” may be
something else) of 0.9 is not unheard of, but pretty high for exterior
envelope glazing
 when I do daylighting/rendering studies I usually go no
higher than 0.8 or so unless I have actual product specs in hand.

 

~Nick

 

 

cid:489575314 at 22072009-0ABB

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: virtual-sim-bounces at lists.onebuilding.org
[mailto:virtual-sim-bounces at lists.onebuilding.org] On Behalf Of Erik
Eriksson
Sent: Monday, September 28, 2009 10:10 AM
To: Paul Carey
Cc: virtual-sim at lists.onebuilding.org
Subject: Re: [Virtual-sim] Low DF-values with Radiance

 


Hey, 

Yeah, I've tried that. With more or less the same result.
I'm quite new to this with lighting calculations. I'm more used to energy
performance. 
So I cant really say if the values are correct or not. 

Best regards 

E r i k   E r i k s s o n 

Energy specialist and project manager
________________________________
White project & environmental management

Box 4700
116 92 STOCKHOLM
Phone: +46(0)8-402 26 77
Fax:      +46 (0)8-402 25 10
Visit:     Östgötagatan 100
 <http://www.white.se/> http://www.white.se

We are certified according to ISO 9000 and 14 001 


From: 

Paul Carey <paul at zed-uk.com> 


To: 

Erik Eriksson <erik.eriksson at white.se> 


Cc: 

"virtual-sim at lists.onebuilding.org" <virtual-sim at lists.onebuilding.org> 


Date: 

2009-09-28 17:06 


Subject: 

Re: [Virtual-sim] Low DF-values with Radiance

 

  _____  




Erik 

Try carrying out a model for one room at a time. The results tend to be
quite different. 

Cheers 
Paul 



Sent from my iPhone 

On 28 Sep 2009, at 15:55, Erik Eriksson <erik.eriksson at white.se> wrote:


Hi all, 

I'm doing some daylighting studies with RadianceIES with a model I've
imported from revit. The model seems to have been imported just fine. 
However I'm getting very low DF-values. 
The rooms I've been studying are rectangular cellular offices with about 12%
of the floor area consisting of windows. 
The results show that approx 5-10% the area of a working plane at 0,8 m
above the floor has a DF-value of 1.2 %. 
This feels like a very low number. The window transparancy is 0,9 and all
the walls are white colored. The ceiling is white and the floor is gray. 

Does anyone have a suggestion as to what might be wrong or if these values
seem ok. 

Thanks in advance 

Best regards 

E r i k   E r i k s s o n 

Energy specialist and project manager
________________________________
White project & environmental management

Box 4700
116 92 STOCKHOLM
Phone: +46(0)8-402 26 77
Fax:      +46 (0)8-402 25 10
Visit:     Östgötagatan 100
 <http://www.white.se/> http://www.white.se

We are certified according to ISO 9000 and 14 001 
_______________________________________________
Virtual-sim mailing list
Virtual-sim at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/virtual-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
VIRTUAL-SIM-UNSUBSCRIBE at ONEBUILDING.ORG 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/virtual-sim-onebuilding.org/attachments/20090929/34e5f59c/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/virtual-sim-onebuilding.org/attachments/20090929/34e5f59c/attachment-0001.jpeg>


More information about the Virtual-sim mailing list