Hi Erik

 

There are couple of suggestions while using the Microflo module of IES.

 

1.	While importing the dxf file into IES, the dxf file should be clear, I mean to say to be a single line file as to avoid picking the points close to one another.
2.	Try to use the grid for the point selection not the end point. As while using the program you can find a difference that while picking up a end point there could be a small variation in the point which will result in a very narrow grid and which will increase the no. of cells and that could led to a problem of the memory and also the convergence will not be achieved and end up with inappropriate results.
3.	IES is simple to use for CFD as it works very well if we have a Maximum aspect ratio <10:1
4.	IES is having a problem, it can't do the internal and external simulation at one instance (in a single go), where as the programs like Phoenics (CHAM software) can do it in one go.

 

May be these points help you in achieving the right results.

Regards

Manjinder Singh

 

Mechanical Engineer | Professional Services Portfolio | Project Services

-----------------------------------------------------------------------------------------

Level 5B 80 George Street,

Brisbane, Queensland 4000

T:   (07) 3227 8064 | F:   (07) 3224 6151

E:   Manjinder.Singh at projectservices.qld.gov.au | Web:  www.projectservices.qld.gov.au <http://www.projectservices.qld.gov.au/> 

 

 

________________________________

From: Erik Eriksson [mailto:erik.eriksson at white.se] 
Sent: Tuesday, 3 March 2009 6:53 PM
To: SINGH Manjinder
Cc: Nouman; virtual-sim at lists.onebuilding.org
Subject: RE: [Virtual-sim] Issues and dxf?

 

Hi Manjinder,

I tested it for a couple of years ago and my experience was that it was very easy to use. That is normally a good thing, but when it comes to CFD programs they tend to be very complicated and I just figured that MicroFlo therefore couldnt be that accurate in its results. 

We are looking into it again and I think its brilliant that its so simple, but the results need to be accurate (obviously). 
Have you found the accuracy in the results doubtful?

Best regards

E r i k E r i k s s o n 

Energy specialist and project manager
________________________________
White project & environmental management

Box 4700
116 92 STOCKHOLM
Phone: +46(0)8-402 26 77
Fax: +46 (0)8-402 25 10
Visit: Östgötagatan 100
http://www.white.se

We are certified according to ISO 9000 and 14 001

 "SINGH Manjinder" ---2009-03-03 00:09:08---Hi Erik

 
From:

 
"SINGH Manjinder" <Manjinder.SINGH at projectservices.qld.gov.au>


To:


"Erik Eriksson" <erik.eriksson at white.se>, "Nouman" <nouman310 at yahoo.com>


Cc:


<virtual-sim at lists.onebuilding.org>


Date:


2009-03-03 00:09


Subject:


RE: [Virtual-sim] Issues and dxf?

________________________________




Hi Erik

Presently I am working on the Microflo module of IES VE for a CFD analysis. What kind of help u need??


Manjinder Singh

Mechanical Engineer | Professional Services Portfolio | Project Services
-----------------------------------------------------------------------------------------
Level 5B 80 George Street,
Brisbane, Queensland 4000
T: (07) 3227 8064 | F: (07) 3224 6151
E: Manjinder.Singh at projectservices.qld.gov.au <mailto:Manjinder.Singh at projectservices.qld.gov.au>  | Web: www.projectservices.qld.gov.au <http://www.projectservices.qld.gov.au/> 

________________________________

From: virtual-sim-bounces at lists.onebuilding.org [mailto:virtual-sim-bounces at lists.onebuilding.org] On Behalf Of Erik Eriksson
Sent: Tuesday, 3 March 2009 2:38 AM
To: Nouman
Cc: virtual-sim at lists.onebuilding.org
Subject: Re: [Virtual-sim] Issues and dxf?

Hi,

ok, I've had some experience with dxf-imports. I did it a couple of years ago and was quite annoyed with it. Has it been improved? 
What I found was that when it found a text it looked around it and if it found walls then that was it, but since you can have different thinkness on the walls and you need to find the outer limit of the outer walls, but VE stops at the inner limit and the middle of the interior walls needs to be found it makes it quite complicated to turn a normal dwg-drawing into a useful one or have you worked out a smart method of doing this?

When i was referering to reliability I was thinking of heat storage (with and without false celings) and solar insolation on more complex surfaces etc. 

Have you had any experience with MicroFlo?

Best regards

E r i k E r i k s s o n 

Energy specialist and project manager
________________________________
White project & environmental management

Box 4700
116 92 STOCKHOLM
Phone: +46(0)8-402 26 77
Fax: +46 (0)8-402 25 10
Visit: Östgötagatan 100
http://www.white.se <http://www.white.se/> 

We are certified according to ISO 9000 and 14 001

Nouman ---2009-03-02 17:21:18---Hi, yes dxf files can be imported in VE and can save tons of time in drawing the building. Please ta 

 
From:

 
Nouman <nouman310 at yahoo.com>


To:


Erik Eriksson <erik.eriksson at white.se>, virtual-sim at lists.onebuilding.org


Date:


2009-03-02 17:21


Subject:


Re: [Virtual-sim] Issues and dxf?

________________________________





Hi,
yes dxf files can be imported in VE and can save tons of time in drawing the building. Please take the following steps before you import any dxf into VE: 

			*	Remove in dxf file everything except: walls,windows, doors and labels 
			*	When you are importing the dxf. make sure, that the appropriate scale has been input. 
			*	The trick to find out scale of the drawing is, to measure a door, typically a single door is 1m, now let say the measurement comes upto be 10m it means its 1:10 scale. etc 

The calculation of VE is reliable. Only that the dynamic calculation gives us actualy true loads which some times differ from ASHRAE loads. The reason is ASHRAE does all its loads on a particualr design day. Whereas VE picks up the worse case scanario for the building. VE also has the capability to somply calculate ASHRAE loads. 

Best Regards;
Ali Nouman Khan

________________________________


From: Erik Eriksson <erik.eriksson at white.se>
To: virtual-sim at lists.onebuilding.org
Sent: Monday, March 2, 2009 8:40:08 AM
Subject: [Virtual-sim] Issues and dxf?

Hi everyone!

I just joined this mail list and I'm curious about how you use this program and if you have found any issues. 
I use it extensivly and I have a few issues with it and I'm afraid that some of the calculation methods arent that reliable. 

I've heard that many users import their geometry by using dxf-files. I've tried this, but I've found it somewhat complicated. 
Do you have any smart methods? What program do you use to create the dxf-files? Autocad?

Best regards

E r i k E r i k s s o n 

Energy specialist and project manager
________________________________
White project & environmental management

Box 4700
116 92 STOCKHOLM
Phone: +46(0)8-402 26 77
Fax: +46 (0)8-402 25 10
Visit: Östgötagatan 100
http://www.white.se <http://www.white.se/> 

We are certified according to ISO 9000 and 14 001 

________________________________


 Yahoo! Canada Toolbar : Search from anywhere on the web and bookmark your favourite sites. Download it now! <http://ca.toolbar.yahoo.com/> 

***************************** Disclaimer ***************************** 

The contents of this electronic message and any attachments are intended only for the addressee and may contain privileged or confidential information. They may only be used for the purposes for which they were supplied. If you are not the addressee, you are notified that any transmission, distribution, downloading, printing or photocopying of the contents of this message or attachments is strictly prohibited. The privilege of confidentiality attached to this message and attachments is not waived, lost or destroyed by reason of mistaken delivery to you. If you receive this message in error please notify the sender by return e-mail or telephone. 

Please note: the Department of Public Works carries out automatic software scanning, filtering and blocking of E-mails and attachments (including emails of a personal nature) for detection of viruses, malicious code, SPAM, executable programs or content it deems unacceptable. All reasonable precautions will be taken to respect the privacy of individuals as outlined in the DPW Privacy Plan. Personal information will only be used for official purposes, e.g. monitoring Departmental Personnel's compliance with Departmental Policies. Personal information will not be divulged or disclosed to others, unless as required by Departmental Policy and/or State or Commonwealth Law. 

Thank you. 


***************************** Disclaimer *****************************

The contents of this electronic message and any attachments are intended only for the addressee and may contain privileged or confidential information. They may only be used for the purposes for which they were supplied. If you are not the addressee, you are notified that any transmission, distribution, downloading, printing or photocopying of the contents of this message or attachments is strictly prohibited. The privilege of confidentiality attached to this message and attachments is not waived, lost or destroyed by reason of mistaken delivery to you. If you receive this message in error please notify the sender by return e-mail or telephone.

Please note: the Department of Public Works carries out automatic
software scanning, filtering and blocking of E-mails and attachments (including emails of a
personal nature) for detection of viruses, malicious code, SPAM, executable programs or content it deems
unacceptable. All reasonable precautions will be taken to respect the privacy of
individuals as outlined in the DPW Privacy Plan. Personal information will only be used for official
purposes, e.g. monitoring Departmental Personnel's compliance with Departmental Policies.
Personal information will not be divulged or disclosed to others, unless as required by Departmental
Policy and/or State or Commonwealth Law.

Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/virtual-sim-onebuilding.org/attachments/20090309/f4de02df/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1076 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/virtual-sim-onebuilding.org/attachments/20090309/f4de02df/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 73 bytes
Desc: image005.gif
URL: <http://lists.onebuilding.org/pipermail/virtual-sim-onebuilding.org/attachments/20090309/f4de02df/attachment-0005.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 73 bytes
Desc: image004.gif
URL: <http://lists.onebuilding.org/pipermail/virtual-sim-onebuilding.org/attachments/20090309/f4de02df/attachment-0006.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 105 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/virtual-sim-onebuilding.org/attachments/20090309/f4de02df/attachment-0007.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 73 bytes
Desc: image007.gif
URL: <http://lists.onebuilding.org/pipermail/virtual-sim-onebuilding.org/attachments/20090309/f4de02df/attachment-0008.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 73 bytes
Desc: image008.gif
URL: <http://lists.onebuilding.org/pipermail/virtual-sim-onebuilding.org/attachments/20090309/f4de02df/attachment-0009.gif>


More information about the Virtual-sim mailing list