    <p>Loïc,</p>
    <p>  The best way to address airflow within a building is to couple
      your Type56 simulation either with TRNFlow or CONTAM (Type97). The
      basic idea is that you build a parallel model to your Type56
      containing information about the airflow openings between the
      airnodes (a radiation zone can contain multiple airnodes,
      especially where there is an atrium like you have described).
      TRNFlow or CONTAM then take the air node temperatures as well as
      the wind speed and geometry of the building and determine the
      amount of air flow that results between the air nodes. Large
      horizontal openings are challenging because both TRNFlow and
      CONTAM treat air flow through a horizontal opening as
      unidirectional. Still, it is by far the most rigorous way of
      treating the situation.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 1/13/2023 8:29 AM, Loic Tachon via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAJ2U-g_8GnZtJpdMkTGrSgbeoMsdf+xhd_bXRjOcaTAQEPnncQ@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">Dear Trnsys community,
        <div><br>
        </div>
        <div>I want to simulate the stack effect in a high room with
          high thermal gain.</div>
        <div><br>
        </div>
        <div>For this, I have 1 zone and 5 thermal air nodes in the z
          direction to get the temperature at several heights.  <br
            clear="all">
          <div><img src="cid:part1.7Rrv1qDc.QZW6KuVa@tess-inc.com"
              alt="image.png" class="" width="243" height="480"><br>
          </div>
          <div>How can I do this and avoid that TRNSYS see ceiling
            between the zone ? Do I need to delete the horizontal
            surface for zone 2-3-4 ? Or do I put mass less horizontal
            surface ?</div>
          <div><br>
          </div>
          <div>As Well, how do I do the cross flow ventilation ? Do I
            use the couple mass flow between zones ?</div>
          <div><img src="cid:part2.QkSxYGPX.tYjJdJtD@tess-inc.com"
              alt="image.png" class="" width="542" height="323"><br>
          </div>
          <div><br>
          </div>
          <div> or I put a coupling air flow (same that natural
            ventilation mass flow) for the horizontal surface ?</div>
          <div><img src="cid:part3.0mO0izuT.bVkgsVwg@tess-inc.com"
              alt="image.png" class="" width="503" height="137"><br>
          </div>
          <div><br>
          </div>
          <div>Thanks a lot. </div>
          <div><br>
          </div>
          <div>Best regards,</div>
          <div><br>
          </div>
          -- <br>
          <div dir="ltr" class="gmail_signature"
            data-smartmail="gmail_signature">
            <div dir="ltr"><font style="font-size:12.8px"
                color="#000000"><b>Dr. Loïc Tachon </b></font>
              <div style="font-size:12.8px">
                <div><font color="#000000">(+33) 6 7440-0536 (France)</font></div>
                <div><br>
                </div>
              </div>
              <div><font color="#e69138"><b><br>
                  </b></font></div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>