    <p>  As far as the initial temperature is concerned, set it in
      between the heating setpoint and cooling setpoint temperature and
      it won't have any impact on what your peak heating and cooling
      loads are. When the zone temperature is between the heating and
      cooling setpoint then by definition there is no load on the space.
      <br>
    </p>
    <p>  As a side note, I would caution against sizing HVAC equipment
      based on a short term simulation. I mention it becuase in long
      term simulations the initial value has little impact and if your
      initial zone temperature does have a significant impact then it
      might be that your simulation is short. In any case, I'd recommend
      running a year or two or at least december plus a year so that any
      initial values that the simulation starts with aren't impacting
      your results. If you're running a case in which you have a lot of
      thermal coupling with the ground and are modeling the ground
      temperature as impacted by the presence of the building (using
      Type49 for example) then you should be running a 5-10 year long
      simulation so as to get away from any initial value bias.</p>
    <p> As for your second question if you impose a humidity setpoint on
      your building then as with temperature, Type56 will limit the
      building's humidity and report the amount of latent energy that
      had to be added or removed in order to keep it between the
      setpoints. <br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 1/9/2023 4:21 PM, Ali Shahrouzian
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:YT2PR01MB9446624CDE59021FE57CBCCE9CFE9@YT2PR01MB9446.CANPRD01.PROD.OUTLOOK.COM">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style>@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;
        mso-fareast-language:EN-US;}a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:#0563C1;
        text-decoration:underline;}a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri",sans-serif;
        color:windowtext;}.MsoChpDefault
        {mso-style-type:export-only;
        font-family:"Calibri",sans-serif;
        mso-fareast-language:EN-US;}div.WordSection1
        {page:WordSection1;}</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal">Dear all TRNSYS user,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Hi,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">I have two questions about estimating the
          size of HVAC system of a building.
          <o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">My 1<sup>st</sup> question:<o:p></o:p></p>
        <p class="MsoNormal">As you know, there is a good explanation in
          09-Tutorial document regarding estimating the size of HVAC
          equipment of a building by using the printegrator component
          (setting its parameter #4 to 15 min and determining the peak
          15-minute heating and cooling load for building). However, it
          is evident that the maximum 15-minute heating and cooling load
          for the building is highly dependent on the initial
          temperature of the building, which is set on TRNBuild. When
          starting a simulation, what should the initial temperature be?<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">My 2<sup>nd</sup> question:<o:p></o:p></p>
        <p class="MsoNormal">How can I estimate the size of humidifier
          or dehumidifier in the HVAC equipment?<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span lang="EN-US">I’d be glad if someone
            could help me out.<o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Best regards,<o:p></o:p></p>
        <p class="MsoNormal">Ali<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><o:p></o:p></p>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>