    <p>László,</p>
    <p>  The capacitance of the walls is definitely taken into account
      although not in the same way that the capacitance of the stuff in
      the zones is taken into account. The walls are made up of layers;
      for each layer you provide the material's density, specific heat,
      and thermal conductivity. Those values as well as the thickness of
      each layer and the order of the layers are used to generate a set
      of values called conduction transfer function coefficients. Those
      coefficients are made for discreet steps backwards in time (like a
      time step but in this case it is called a time base). If there is
      a mismatch between the time constant of your wall and the timebase
      that you have selected (in the "outputs" window of TRNBuild) then
      I suppose that changes in the capacitance of the walls might not
      show up in the results. Say for example you have selected a 1hr
      timebase but the wall has a low thermal capacitance such that its
      time constant is more like 15 minutes. Changes to the capacitance
      that don't significantly extend the time constant of the wall
      might not show in the results. <br>
    </p>
    <p>  You can also get into some problems if you have a high thermal
      capacitance wall, which sometimes you have to treat as "resistive
      only" in TRNBuild due to the way that the conduction transfer
      function coefficients are generated. If you have had to treat the
      wall as a thermal resistance then the capacitance doesn't enter
      into the treatment of the walls.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <p><br>
    </p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 07/25/2022 05:42, Gergely László
      Zsolt wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:PR3P195MB0473DDE40EFA2E7260CD7C40BF959@PR3P195MB0473.EURP195.PROD.OUTLOOK.COM">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <style type="text/css" style="display:none;">P {margin-top:0;margin-bottom:0;}</style>
      <div style="font-family: Calibri, Arial, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
        Dear All,<br>
        <br>
        Still need your help with this.<br>
        Running some simulations changing capacitance values (despite
        the manual mentions that this value stands for the air and the
        furnitures and walls shall not be considered here) of the
        airnode and capacitance of the layers I am not convinced that
        calculations consider the capacitance of the walls!<br>
        <br>
        Could you help me out?</div>
      <div style="font-family: Calibri, Arial, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
        <br>
      </div>
      <div style="font-family: Calibri, Arial, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
        Regards,</div>
      <div>
        <div style="font-family: Calibri, Arial, Helvetica, sans-serif;
          font-size: 12pt; color: rgb(0, 0, 0);">
          <br>
        </div>
        <div id="Signature">
          <div>
            <div style="font-family: Calibri, Arial, Helvetica,
              sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
              <div style="margin:0px;font-size:12pt"><span
                  style="margin:0px;font-size:10pt;font-family:"Sitka
                  Heading", Cochin, serif;color:rgb(134, 17,
                  6);text-align:start;background-color:white"><b>László
                    GERGELY</b></span><br>
                <span
                  style="margin:0px;font-size:10pt;font-family:"Sitka
                  Heading", Cochin, serif;color:rgb(134, 17,
                  6);text-align:start;background-color:white">PhD stude</span><span
style="margin:0px;font-size:10pt;font-family:"Sitka Heading",
                  Cochin, serif;color:rgb(134, 17, 6)">nt, Building
                  Energy Engineering</span></div>
              <div style="margin:0px;font-size:12pt"><span
                  style="margin:0px;font-size:10pt"></span><span
                  style="margin:0px;font-size:10pt;font-family:"Sitka
                  Heading", Cochin, serif;color:rgb(134, 17,
                  6);text-align:start;background-color:white">Budapest </span><span
style="margin:0px;font-size:10pt;font-family:"Sitka Heading",
                  Cochin, serif;color:rgb(134, 17, 6)">University of
                  Technology and Economics</span></div>
              <span style="margin:0px;font-size:12pt"><img
                  style="margin:0px;font-size:16px;width:129px;height:41px;max-width:100%"
                  data-outlook-trace="F:1|T:1"
                  src="cid:part1.Jvg6f0xo.U3HNSdZY@tess-inc.com"
                  class="" width="129" height="41"></span><br>
            </div>
          </div>
        </div>
      </div>
      <hr style="display:inline-block;width:98%" tabindex="-1">
      <div id="divRplyFwdMsg" dir="ltr"><font style="font-size:11pt"
          face="Calibri, sans-serif" color="#000000"><b>Feladó:</b>
          TRNSYS-users
          <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-bounces@lists.onebuilding.org"><trnsys-users-bounces@lists.onebuilding.org></a>,
          meghatalmazó: Gergely László Zsolt via TRNSYS-users
          <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@lists.onebuilding.org"><trnsys-users@lists.onebuilding.org></a><br>
          <b>Elküldve:</b> 2022. július 22., péntek 17:48<br>
          <b>Címzett:</b> TRNSYS users mailing list at OneBuilding.org
          <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@lists.onebuilding.org"><trnsys-users@lists.onebuilding.org></a>; David BRADLEY
          <a class="moz-txt-link-rfc2396E" href="mailto:d.bradley@tess-inc.com"><d.bradley@tess-inc.com></a><br>
          <b>Másolatot kap:</b> Gergely László Zsolt
          <a class="moz-txt-link-rfc2396E" href="mailto:gergely.laszlo@gpk.bme.hu"><gergely.laszlo@gpk.bme.hu></a><br>
          <b>Tárgy:</b> [TRNSYS-users] Type 56 thermal mass</font>
        <div> </div>
      </div>
      <style type="text/css" style="display:none">p
        {margin-top:0;
        margin-bottom:0}</style>
      <div dir="ltr">
        <div class="x_elementToProof"
          style="font-family:Calibri,Arial,Helvetica,sans-serif;
          font-size:12pt; color:rgb(0,0,0)">
          Dear All,<br>
        </div>
        <div class="x_elementToProof"
          style="font-family:Calibri,Arial,Helvetica,sans-serif;
          font-size:12pt; color:rgb(0,0,0)">
          <br>
          For some reasons I believe that my simulations do not consider
          thermal capacitance of my building.<br>
          I have no idea what goes wrong... I thought about overwriting
          the capacitance value of the zones however based on the
          documentation that value shall not include wall capacitance.<br>
          <br>
          In the enclosed project there is a nightime setback and the
          problem is visible as the temperature drops as soon as the
          heating is off and rises as soon as it is on.<br>
          <br>
          To make things in context the aim of the project is testing
          different options reducing heating demand.</div>
        <div class="x_elementToProof"
          style="font-family:Calibri,Arial,Helvetica,sans-serif;
          font-size:12pt; color:rgb(0,0,0)">
          <br>
        </div>
        <div class="x_elementToProof"
          style="font-family:Calibri,Arial,Helvetica,sans-serif;
          font-size:12pt; color:rgb(0,0,0)">
          Do you have any suggestions for overcoming the problem?<br>
          I would be grateful!</div>
        <div class="x_elementToProof"
          style="font-family:Calibri,Arial,Helvetica,sans-serif;
          font-size:12pt; color:rgb(0,0,0)">
          <br>
        </div>
        <div class="x_elementToProof"
          style="font-family:Calibri,Arial,Helvetica,sans-serif;
          font-size:12pt; color:rgb(0,0,0)">
          Thanks in advance,</div>
        <div>
          <div style="font-family:Calibri,Arial,Helvetica,sans-serif;
            font-size:12pt; color:rgb(0,0,0)">
            <br>
          </div>
          <div id="x_Signature">
            <div>
              <div
                style="font-family:Calibri,Arial,Helvetica,sans-serif;
                font-size:12pt; color:rgb(0,0,0)">
                <div style="margin:0px; font-size:12pt"><span
                    style="margin:0px; font-size:10pt;
                    font-family:"Sitka Heading",Cochin,serif;
                    color:rgb(134,17,6); text-align:start;
                    background-color:white"><b>László GERGELY</b></span><br>
                  <span style="margin:0px; font-size:10pt;
                    font-family:"Sitka Heading",Cochin,serif;
                    color:rgb(134,17,6); text-align:start;
                    background-color:white">PhD stude</span><span
                    style="margin:0px; font-size:10pt;
                    font-family:"Sitka Heading",Cochin,serif;
                    color:rgb(134,17,6)">nt, Building Energy Engineering</span></div>
                <div style="margin:0px; font-size:12pt"><span
                    style="margin:0px; font-size:10pt"></span><span
                    style="margin:0px; font-size:10pt;
                    font-family:"Sitka Heading",Cochin,serif;
                    color:rgb(134,17,6); text-align:start;
                    background-color:white">Budapest </span><span
                    style="margin:0px; font-size:10pt;
                    font-family:"Sitka Heading",Cochin,serif;
                    color:rgb(134,17,6)">University of Technology and
                    Economics</span></div>
                <span style="margin:0px; font-size:12pt"><img
                    style="margin:0px; font-size:16px; width:129px;
                    height:41px; max-width:100%"
                    data-outlook-trace="F:2|T:2"
                    src="cid:part2.B1KQC11W.t9TP7xJS@tess-inc.com"
                    class="" width="129" height="41"></span><br>
              </div>
            </div>
          </div>
        </div>
      </div>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>