    <p>Pu,</p>
    <p> I can imagine some configurations of nine airnodes that might
      not result in getting same value of SQCOOL as QCOOL when those
      nine airnodes are combined into one especially as concerns
      radiation exchange between the surfaces. I would suggest you send
      your *.tpf and *.b18 to your distributor so that they can check to
      see if there is not some assumption difference that is causing the
      results that you are seeing. <br>
    </p>
    <p> It might be worth reading a bit in the Type56/TRNBuild
      documentation about GEOSURF. That variable specifies the fraction
      of beam radiation entering a zone that falls on each surface of
      the zone. I am not very familiar with the details of how the
      default value of GEOSURF is determined. It is of course a function
      of the building geometry and not something that should be modified
      in order to bring the results of one model closer to those of
      another.   <br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 07/01/2022 21:54, Huijie Pu via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:2072736e.658.181bcd51e33.Coremail.huijiepu@163.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div
        style="line-height:1.7;color:#000000;font-size:14px;font-family:Arial">
        <div style="line-height: 1.7;">
          <div style="color: rgb(0, 0, 0); font-family: Arial;
            font-size: 14px; margin: 0px;">Hello!</div>
          <div style="margin: 0px;">
            <div style="color: rgb(0, 0, 0); font-family: Arial;
              font-size: 14px; margin: 0px;"><br>
            </div>
            <div style="color: rgb(0, 0, 0); font-family: Arial;
              font-size: 14px; margin: 0px;">I divided a large space
              into nine areas, i.e. in TRNBuild, one zone with nine
              airnodes, but the output NTYPES33-SQCOOL value of the
              model is always higher than the output NTYPES31-QCOOL
              value of the full large space model, but according to the
              actual , the two values should be the same. Both models
              have the same settings, neither have any gains set, and
              the weather files are the same. I don't understand what is
              causing this?</div>
            <div style="margin: 0px;">I found that the difference
              between these two values is related to the GEOSURF values
              of walls and windows, and is most related to the value of
              GEOSURF for wall with boundary conditions that the wall is
              the floor.  The sum of the GEOSURF  values of each airnode
              is 1. So that the cooling demand value of the two models
              is the same, which is need to modify the geosurf value of
              each air node?</div>
            <div style="color: rgb(0, 0, 0); font-family: Arial;
              font-size: 14px; margin: 0px;"><br>
            </div>
            <div style="color: rgb(0, 0, 0); font-family: Arial;
              font-size: 14px; margin: 0px;">kind regards,</div>
            <div style="color: rgb(0, 0, 0); font-family: Arial;
              font-size: 14px; margin: 0px;">Pu</div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>