<div dir="ltr">Hi Hassan,<div><br></div><div>Thanks for your reply. </div><div><br></div><div>What is the difference between THERMAL CONDUCTANCE, U=    37.80000 kJ/h m2K; U-Wert=     3.77020 W/m2K ? (we find theses wall value in the inf file) This is not just unit conversion because 37.8 / 3.6 is different that 3.77.</div><div><br></div><div>Thanks for the help.</div><div><br></div><div>Best regards,</div><div><br></div><div><br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">Le mar. 5 juil. 2022 à 10:36, Mahach, Hassan <<a href="mailto:mahach@izes.de">mahach@izes.de</a>> a écrit :<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">





<div lang="DE">
<div class="gmail-m_5913672376163770652WordSection1">
<p class="MsoNormal"><span style="font-size:11pt;font-family:"Comic Sans MS";color:rgb(31,73,125)">Hi Dr. Tachon,
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:"Comic Sans MS";color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11pt;font-family:"Comic Sans MS";color:rgb(31,73,125)">The U-Wert means how your wall transfer the heat and it’s normal that you get this change because you changed the thickness
 of your materials as well as his type (U-wert= Thermal conductivity/thickness). You may also consider your ground-on-slab as boundary wall by setting  to the inside (front) and outside (back) convective heat transfer coefficients. You can refer to volume,
 page 143 of the documentation<u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US" style="font-family:Arial,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><i><span lang="EN-US" style="font-size:11pt;font-family:Arial,sans-serif">“</span></i><i><span lang="EN-US" style="font-size:11pt">WALLS WITH KNOWN BOUNDARY CONDITION<u></u><u></u></span></i></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><i><span lang="EN-US" style="font-size:11pt">A wall having a known boundary condition might be a concrete floor resting on ground of a known temperature or a wall adjacent to a zone whose temperature is known. The front of the wall is
 considered to be at the inside of the zone. Normally, the boundary condition is the temperature of a node connected to the back surface of the wall through a pure resistance. It is possible to specify the surface temperature of the outside by setting the back
 side heat transfer coefficient of the WALL Type (HBACK) to a very small value (<b>less than 0.001 kJ/h/m²).</b> This WALL Type is then only appropriate for use as a wall with a known boundary. The use of a very small value may be confusing but was kept for
 backwards compatibility reasons”<u></u><u></u></span></i></p>
<p class="MsoNormal"><i><span lang="EN-US"><u></u> <u></u></span></i></p>
<p class="MsoNormal"><i><span lang="EN-US" style="font-size:11pt;font-family:"Comic Sans MS";color:rgb(31,78,121)">I Hope that’s helps
<u></u><u></u></span></i></p>
<p class="MsoNormal"><i><span lang="EN-US" style="font-size:11pt;font-family:"Comic Sans MS";color:rgb(31,78,121)">Hassan
</span></i><i><span lang="EN-US" style="font-size:10pt;font-family:"Comic Sans MS";color:rgb(31,78,121)"><u></u><u></u></span></i></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span lang="EN-US" style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:black">Dr. Hassan Mahach</span></b><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:black"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black">wissenschaftlicher Mitarbeiter<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black">Arbeitsfeld Technische Innovationen<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black">+49 681 844 972 23<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black"><a href="mailto:mahach@izes.de" target="_blank">mahach@izes.de</a><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black"><a href="http://www.izes.de" target="_blank">www.izes.de</a><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black">IZES gGmbH | Altenkesseler Straße 17, Geb. A1 | 66115 Saarbrücken<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black">Büro Berlin | Albrechtstraße 22 | 10117 Berlin<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black">Telefon: +49 681 844 972 0 | Fax: +49 681 761 799 9<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black">Rechtsform: gGmbH | Registergericht Saarbrücken HRB 8499<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black">Steuernummer: 040 140 241 53 | USt.-IdNr.: DE 138 113 796<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black">Aufsichtsratsvorsitz: Minister Jürgen Barke<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black">Geschäftsführung: Prof. Frank Baur | Dr. Lesya Matiyuk<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black"><img width="394" height="74" id="gmail-m_5913672376163770652Grafik_x0020_1" src="cid:181ce7713ea4ce8e91" alt="cid:image001.jpg@01D8905B.2921E320"></span><span style="font-size:9pt;font-family:Calibri,sans-serif;color:black"><u></u><u></u></span></p>
<p class="MsoNormal"><span><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif">Von:</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"> TRNSYS-users [mailto:<a href="mailto:trnsys-users-bounces@lists.onebuilding.org" target="_blank">trnsys-users-bounces@lists.onebuilding.org</a>]
<b>Im Auftrag von </b>Loic Tachon via TRNSYS-users<br>
<b>Gesendet:</b> Dienstag, 5. Juli 2022 09:38<br>
<b>An:</b> TRNSYS users mailing list at OneBuilding.org <<a href="mailto:trnsys-users@lists.onebuilding.org" target="_blank">trnsys-users@lists.onebuilding.org</a>><br>
<b>Cc:</b> Loic Tachon <<a href="mailto:dr.loic.tachon@gmail.com" target="_blank">dr.loic.tachon@gmail.com</a>><br>
<b>Betreff:</b> [TRNSYS-users] TRNSYS ground floor<u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal">Dear users,<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">I want to simulate a huge building (5500 m2) with a 20 cm concrete ground without isolation. <u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">I don't really understand how the direct contact boundary condition works.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">I made a ground wall composed of 20 cm of concret and 80 cm of calcar.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">I realize that the simulation result (Tzone temperature) is very dependent of the ground temperature boundary condition. <u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">I use type 77 with the depth of ground temperature of 1m, the amplitude of 12 and the mean temperature of 12.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">If I change the parameters of type 77, the zone temperature results change a lots.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">In the inf file, i get u value result of my floor : THERMAL CONDUCTANCE, U=     4.21086 kJ/h m2K; U-Wert=     0.97567 W/m2K<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">If I don't put the 80 cm of calcar, I get the following u value :<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">THERMAL CONDUCTANCE, U=    37.80000 kJ/h m2K; U-Wert=     3.77020 W/m2K<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Is this normal ? What means U-Wert ?<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<p class="MsoNormal"><br clear="all">
<u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<p class="MsoNormal">-- <u></u><u></u></p>
<div>
<div>
<p class="MsoNormal"><b><span style="font-size:9.5pt;color:black">Dr. Loïc Tachon </span></b><u></u><u></u></p>
<div>
<div>
<p class="MsoNormal"><span style="font-size:9.5pt;color:black">(+33) 6 7440-0536 (France)</span><span style="font-size:9.5pt"><u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:9.5pt"><u></u> <u></u></span></p>
</div>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>
</div>
</div>

</blockquote></div><br clear="all"><div><br></div>-- <br><div dir="ltr" class="gmail_signature"><div dir="ltr"><font style="font-size:12.8px" color="#000000"><b>Dr. Loïc Tachon </b></font><div style="font-size:12.8px"><div><font color="#000000">(+33) 6 7440-0536 (France)</font></div><div><br></div></div><div><font color="#e69138"><b><br></b></font></div></div></div>