    <p>Jacopo,</p>
    <p>  I think you would take the energy transfer outputs from the
      radiant floor model and impose them on Type690 as part of the
      sensible load on the space. Basically your radiant floor would
      augment or diminish the instantaneous gains that are already
      computed for your space.<br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 05/18/2022 09:21, Jacopo Valente
      wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:DB6PR06MB395984B7FACB407FF2E0D208A6D19@DB6PR06MB3959.eurprd06.prod.outlook.com">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style>@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}pre
        {mso-style-priority:99;
        mso-style-link:"Preformattato HTML Carattere";
        margin:0cm;
        font-size:10.0pt;
        font-family:"Courier New";
        color:black;}span.PreformattatoHTMLCarattere
        {mso-style-name:"Preformattato HTML Carattere";
        mso-style-priority:99;
        mso-style-link:"Preformattato HTML";
        font-family:"Courier New";
        color:black;}.MsoChpDefault
        {mso-style-type:export-only;}div.WordSection1
        {page:WordSection1;}</style>
      <div class="WordSection1">
        <p class="MsoNormal">Thank you for your suggestion. I understand
          the idea to have a lump capacitance to represent the zone and
          then control its temperature. However, I only know the type
          690 which input refers to an air flow rate. Is there a
          corresponding type to use in a water-water heat pump, so with
          a water flow rate?<span lang="EN-GB"><o:p></o:p></span></p>
        <p class="MsoNormal">Thank you again.<br>
          <br>
          kind regards,<br>
          <br>
          Jacopo</p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div
          style="mso-element:para-border-div;border:none;border-top:solid
          #E1E1E1 1.0pt;padding:3.0pt 0cm 0cm 0cm">
          <p class="MsoNormal" style="border:none;padding:0cm"><b>Da: </b><a
              href="mailto:d.bradley@tess-inc.com"
              moz-do-not-send="true">David BRADLEY</a><br>
            <b>Inviato: </b>lunedì 16 maggio 2022 20:00<br>
            <b>A: </b><a
              href="mailto:trnsys-users@lists.onebuilding.org"
              moz-do-not-send="true">TRNSYS users mailing list at
              OneBuilding.org</a><br>
            <b>Cc: </b><a href="mailto:jacopovalente@LIVE.IT"
              moz-do-not-send="true">Jacopo Valente</a><br>
            <b>Oggetto: </b>Re: [TRNSYS-users] water-water heat pump
            simulation</p>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p>Jacopo,</p>
        <p> This is a little bit tricky; the problem is that the loads
          you have are presumably instantaneous heating and cooling
          loads. If your delivery device were something without a lot of
          thermal mass (like zonal heat pumps or some fan coils) then I
          would recommend that you impose the loads directly onto the
          liquid stream. However, the radiant floor has a lot of thermal
          mass of its own. I think the best approach would be to impose
          your loads on a lumped capacitance that is tuned to mimic the
          zone. Then you can define a radiant floor using Type653 in
          order to control the temperature of the lumped capacitance
          that has your original building loads imposed upon it.</p>
        <p>kind regards,</p>
        <p> David</p>
        <p><o:p> </o:p></p>
        <div>
          <p class="MsoNormal"><span style="color:black">On 05/16/2022
              09:16, Jacopo Valente via TRNSYS-users wrote:<o:p></o:p></span></p>
        </div>
        <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
          <p class="MsoNormal" style="margin-bottom:12.0pt"><span
              style="color:black">Dear trnsys users,<o:p></o:p></span></p>
          <p class="MsoNormal"><span style="color:black">I’m simulating
              a ground water source heat pump for residential
              conditioning system. I have the hourly load profile of the
              building and i’m not using the type56. However my system
              has radiant floor as emmiter and i see that it’s possible
              to use type653 only with building type56. </span><span
              style="font-family:"Cambria
              Math",serif;color:black">I’m looking for a way to
              simulate this kind of implant, i try with type 690 but i’m
              not sure it’s right for a water system. Any suggestions to
              simulate my implant without type56?<br>
              <br>
              Thank you every all<br>
            </span><span style="color:black"><br>
              Best regards,<br>
              Jacopo Valente<o:p></o:p></span></p>
          <p class="MsoNormal"><span style="color:black"><br>
              <br>
              <o:p></o:p></span></p>
          <pre>_______________________________________________</pre>
          <pre>TRNSYS-users mailing list</pre>
          <pre><a href="mailto:TRNSYS-users@lists.onebuilding.org" moz-do-not-send="true" class="moz-txt-link-freetext">TRNSYS-users@lists.onebuilding.org</a></pre>
          <pre><a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a></pre>
        </blockquote>
        <pre>-- </pre>
        <pre>***************************</pre>
        <pre>David BRADLEY</pre>
        <pre>Principal</pre>
        <pre>Thermal Energy System Specialists, LLC</pre>
        <pre>3 North Pinckney Street - suite 202</pre>
        <pre>Madison, WI  53703 USA</pre>
        <pre><o:p> </o:p></pre>
        <pre>P:+1.608.274.2577</pre>
        <pre><a href="mailto:d.bradley@tess-inc.com" moz-do-not-send="true" class="moz-txt-link-freetext">d.bradley@tess-inc.com</a></pre>
        <pre><o:p> </o:p></pre>
        <pre><a href="http://www.tess-inc.com" moz-do-not-send="true" class="moz-txt-link-freetext">http://www.tess-inc.com</a></pre>
        <pre><a href="http://www.trnsys.com" moz-do-not-send="true" class="moz-txt-link-freetext">http://www.trnsys.com</a></pre>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Courier
            New";color:black"><o:p> </o:p></span></p>
      </div>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>