<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <p>Jacopo,</p>
    <p> This is a little bit tricky; the problem is that the loads you
      have are presumably instantaneous heating and cooling loads. If
      your delivery device were something without a lot of thermal mass
      (like zonal heat pumps or some fan coils) then I would recommend
      that you impose the loads directly onto the liquid stream.
      However, the radiant floor has a lot of thermal mass of its own. I
      think the best approach would be to impose your loads on a lumped
      capacitance that is tuned to mimic the zone. Then you can define a
      radiant floor using Type653 in order to control the temperature of
      the lumped capacitance that has your original building loads
      imposed upon it.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 05/16/2022 09:16, Jacopo Valente via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:DB6PR06MB39590BFD45660F79142D35CDA6CF9@DB6PR06MB3959.eurprd06.prod.outlook.com">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style>@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}.MsoChpDefault
        {mso-style-type:export-only;}div.WordSection1
        {page:WordSection1;}</style>
      <div class="WordSection1">
        <p class="MsoNormal">Dear trnsys users,<br>
          <br>
        </p>
        <p class="MsoNormal">I’m simulating a ground water source heat
          pump for residential conditioning system. I have the hourly
          load profile of the building and i’m not using the type56.
          However my system has radiant floor as emmiter and i see that
          it’s possible to use type653 only with building type56. <span
            style="font-family:"Cambria Math",serif">
            I’m looking for a way to simulate this kind of implant, i
            try with type 690 but i’m not sure it’s right for a water
            system. Any suggestions to simulate my implant without
            type56?<br>
            <br>
            Thank you every all<br>
          </span><br>
          Best regards,<br>
          Jacopo Valente</p>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>