    <p>Sachin,</p>
    <p>  One way to handle this would be to activate an external shading
      factor on the affected windows in TRNBuild. You can set the factor
      to be an input to Type56 and then use an equation or write a
      component to determine the fraction of solar blocked by your
      motorized shading device and its controls. It might be good to
      start by running the building once with no external shading device
      (just building self-shading) and then to run it once with some
      idealized form of your motorized shading (block all beam radiation
      after noon or something) to see the magnitude of the impact that
      shading the windows will have before you spend a lot of time
      developing an equation or a component to model the actual shading
      device.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 03/14/2022 00:17, sachin dahal via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CANRg-FENTJ2fTQ=MouJSWQm6WWz-P13icTdwGJ6MpxiK=8hb-A@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">Dear All,
        <div>             I hope you are safe and doing great. I am a
          student and for my research I need to model a set of motorized
          shading slats in the building model for optimization. Is there
          any guide or manual for modelling such thing in shading zone? </div>
        <div>Please provide instructions in steps. </div>
        <div><br>
        </div>
        <div>Thank You.</div>
        <div>Sachin Dahal</div>
        <div>KMUTT.</div>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>