<div dir="auto">Dear David</div><div dir="auto">For this time, I have the model 3D (with sketchup 2018)of my building but with the extension .Skp not .idf</div><div dir="auto">The model 3D  I have was drawn considering just architectural data without taking in account the thermal zoning! Is there a way to convert the file .SKp to .idf for a simulation with trnsys18, giving that my building is complex and large!?</div><div dir="auto">Thank you in advance</div><div dir="auto"><br></div><div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Fri, 20 Nov 2020 at 15:25 David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-style:solid;padding-left:1ex;border-left-color:rgb(204,204,204)">
  
    
  
  <div>
    <p>Souad,</p>
    <p> I believe that there is a way of opening a 2d dwg as a
      background image in SketchUp so that you can then trace over it
      more quickly than if you were to start from nothing. Still, each
      time that I have encountered this issue I have found that it takes
      juat about the same amount of time if fight with and correct an
      automatic import or if you start from nothing. <br>
    </p>
    <p> Here are a few tips that might help.</p>
    <p>1. use as few thermal zones as possible on each floor. Often you
      can group together rooms that face a certain direction (i.e. have
      a particular sun exposure) into a single thermal zone.</p>
    <p>2. model the plenum between floors as its own zone; this makes it
      much easier to deal with the zone adjacencies from one floor to
      the next.</p>
    <p>3. rely heavily on the line drawing tool. Draw the perimeter of
      each thermal zone's floor then draw vertical lines for the corners
      then connect their tops. I have run into a lot of frustrations
      with the extrude tool.</p>
    <p>4. where possible avoid copying and pasting zones. It is nearly
      as fast to draw another floor perimeter and walls. When I try
      copying and pasting I sometimes have trouble with SketchUp
      selecting things that aren't part of the zone that I am trying to
      copy.</p>
    <p>5. do all the walls floor by floor first and then add windows
      after you have all the walls completed.</p>
    <p>6. import the *.idf into TRNBuild and check adjacencies early and
      often. I don't usually do more than 3 or 4 zones before I save the
      *.idf, import it into TRNBuild, check it and then increase the
      version number in the name of my *.idf file. When you run into
      import errors I find it is often easier just to start over and
      redraw a few zones than it is to figure out where the error is.</p>
    <p>7. this one is rather specific but if you are drawing opaque
      doors (i.e. walls contained within another wall) make a vertical
      line between the middle of the door lintel and the ceiling. This
      will break the containing wall into two walls and while that adds
      another surface for Type56 to deal with I have found that it
      avoids a lot of wall area calculation issues and errors in the
      *.idf file.</p>
    <p>best,</p>
    <p> David</p></div><div>
    <p>  <br>
    </p>
    <p><br>
    </p>
    <p>On 11/20/2020 06:50, Lakjiri Souad via TRNSYS-users wrote:</p>
    </div><div><blockquote type="cite"></blockquote></div><div><blockquote type="cite">
      
      <span style="word-spacing:1px;color:rgb(49,49,49)">Dear Trnsys
        users,</span>
      <div style="font-size:1rem;word-spacing:1px;color:rgb(49,49,49)" dir="auto">I want to simulate a complex building by TRnsys 18.I
        have the plans of the building drawn in 2D by Autocad2020 .</div>
      <div style="font-size:1rem;word-spacing:1px;color:rgb(49,49,49)" dir="auto">What are the possible and easy ways to generate and
        insert the 3 D building in TRnbuild18 using the 2 D autocad 2020
        plans? knowing that The building is large and it would take a
        lot of time if we use the sketchup18 to model it in 3D .</div>
      -- <br>
      <div dir="ltr" data-smartmail="gmail_signature">
        <div dir="ltr">
          <div>
            <div dir="ltr">
              <div>
                <div dir="ltr">
                  <div>
                    <div dir="ltr">Souad Lakjiri
                      <div>Electrical Project Engineer</div>
                      <div>Morocco's Ministry of Health</div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset></fieldset>
      </blockquote></div><div><blockquote type="cite"><pre style="font-family:monospace">_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank" style="font-family:monospace">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank" style="font-family:monospace">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre cols="72" style="font-family:monospace">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank" style="font-family:monospace">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank" style="font-family:monospace">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank" style="font-family:monospace">http://www.trnsys.com</a></pre>
  </div>

</blockquote></div></div>-- <br><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr">Souad Lakjiri<div>Electrical Project Engineer</div><div>Morocco's Ministry of Health</div></div></div></div></div></div></div></div></div>