<p>Paris,</p>
<p> If you ignore one or more walls then in essence you have
assumed that those walls are adiabatic and don't transfer any
energy. An open or screened "wall" will transfer quite a lot of
energy but primarily by convection. I would account for the wall
and make it a single massless, low thermal resistance layer then
spend some time working out how much infiltration air is going to
come through that wall. <br>
</p>
<p> As for the floor, a building sitting on ground will still
transfer some energy to/from the ground beneath. I'd treat the
floor of your greenhouse as some thickness of soil (perhaps
5-10cm) and as a BOUNDARY surface in TRNBuild. There are a few
accepted methods for determining the temperature of the ground
beneath the thin soil layer. You might look at the use of Type49;
it is probably the most rigorous in your case.</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<div class="moz-cite-prefix">On 09/16/2021 14:18, Paris Pasqualin
via TRNSYS-users wrote:<br>
</div>
<blockquote type="cite"
cite="mid:ce728439d64a412c870b214b33db27c2@student.bham.ac.uk">
<meta http-equiv="Content-Type" content="text/html;
charset=windows-1252">
<meta name="Generator" content="Microsoft Word 15 (filtered
medium)">
<style>@font-face
{font-family:"MS Mincho";
panose-1:2 2 6 9 4 2 5 8 3 4;}@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}@font-face
{font-family:"\@MS Mincho";
panose-1:2 2 6 9 4 2 5 8 3 4;}p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0cm;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri",sans-serif;}span.EmailStyle17
{mso-style-type:personal-compose;
font-family:"Calibri",sans-serif;
color:windowtext;}.MsoChpDefault
{mso-style-type:export-only;
font-family:"Calibri",sans-serif;}div.WordSection1
{page:WordSection1;}</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal"><span lang="EN-US">Hello everyone,<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
<p class="MsoNormal"><span lang="EN-US">if I create a building
in trnbuild and I don’t add a wall on certain direction,
does trnbuild understand that there is no wall and will make
the calculations based on that? The same goes for the flour.
To be more specific, I have to build a greenhouse and on one
side the greenhouse is open and covered with an insect proof
net (which shouldn’t have any effect on the thermal
calculations). The greenhouse also doesn’t have a floor. Can
I create the greenhouse without adding the wall and the
flour or I should adopt some “tricks”? <o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
<p class="MsoNormal"><span lang="EN-US">Best regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-US">Paris<o:p></o:p></span></p>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>