    <p>Jim,</p>
    <p> It is normal that Type997 is slow; it is solving a finite
      difference problem for the entire ground field. The model will run
      particularly slowly at the beginning of your simulation but will
      increase in solving speed to some extent as it gets farther in
      (and as the changes in the ground field from one timestep to the
      next diminish). You can speed the model up to some extent by
      increasing the size of your smallest soil node and increasing the
      value of the node size multiplier. The point of Type997, though it
      to provide a rigorous and stable solution. Type952 models a single
      buried pipe rather than a network of pipes. We use it (or its
      twin-conductor cousin) to model the runouts to and from the ground
      field.</p>
    <p>You have to be a bit careful if if your ground field is actually
      buried air ducts rather than pipes containing a liquid. Both
      Type952 and 997 make the assumption that the thermal properties
      (density, specific heat, etc.) are constant over the working
      temperature range, which isn't always a great assumption with air.
      This is particularly true if there is a chance that the water
      vapor in the air condenses as it goes through the ground field.
      There are models available (Transsolar's Type460 for example) that
      are designed to model underground hypocausts such as the one it
      sounds like you are modeling. If indeed air is your working fluid,
      I would recommend using one of those models in place of either 997
      or 952.<br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 09/09/2021 12:45, dimitris soukoulis
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:VI1PR08MB35030D1749DAB500167AC7A6A7D59@VI1PR08MB3503.eurprd08.prod.outlook.com">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-7">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style>@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}.MsoChpDefault
        {mso-style-type:export-only;}div.WordSection1
        {page:WordSection1;}</style>
      <div class="WordSection1">
        <p class="MsoNormal"><span lang="EN-US">Hello everybody,<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">I am simulating a
            multizone building with four separately air-conditioned
            zones (apartments). So far I was working with the 954 air
            source heat pump ( four of them. One for each zone ) but my
            goal was to have a ground source heat pump system connected
            to the building. I tried using the type 997 Horizontal
            ground heat exchanger and connect its outlet flowrate to the
            inlet of each air source heat pump, but  my simulation
            became extremely slow. I am now experimenting with the type
            952 buried horizontal pipe, setting the average surface
            temperature equal to the annual average ambient temperature.
            I also want to change the working fluid from water (default)
            to air so I can directly feed it into the 954 air source
            heat pump. This set-up is significantly faster than before,
            but I am having doubts about its correctness. Any idea,
            suggestion or advice will be greatly appreciated.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">And one last question.
            Is there any standard way of calculating a heat pumps air
            flow rate, or is it just trial and error ?<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Thanks a lot in advance.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Kind regards ,<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Jim Soukoulis <o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">National Technical
            University of Athens.</span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Στάλθηκε από την <a
            href="https://go.microsoft.com/fwlink/?LinkId=550986"
            moz-do-not-send="true">
            Αλληλογραφία</a> για τα Windows</p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>