<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html;
      charset=windows-1252">
  </head>
  <body>
    <p>Jim,</p>
    <p> Your project connections are correct. I think your description
      of the building sounds reasonable too. I can't be 100% sure that
      the implementation is correct as I would need the look in the
      *.b18 file as well.</p>
    <p><br>
    </p>
    <p> The issues that you are running into with the heat pump and
      building are almost always caused by using too long a timestep
      (this should be on the order of 1 to 5 minutes) and/or a heat pump
      that is not sized correctly for the zone that it is serving. I'm
      not sure how you have handled the conditioning in the zones that
      are not served by the heat pump but I would recommend putting them
      into energy rate control while you are adding heat pumps. Each
      time you add a heat pump to a zone you'll want to turn off that
      zone's automatic/idealized heating and cooling. The problem is
      that if all but one zone is unconditioned, the additional load on
      the one conditioned zone (from all of its unconditioned neighbors)
      causes the heat pump to be undersized until the neighboring zones
      are also conditioned.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <p><br>
    </p>
    <p><br>
    </p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 08/26/2021 15:47, dimitris soukoulis
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:VI1PR08MB35032C44E4A761932C7B5691A7C79@VI1PR08MB3503.eurprd08.prod.outlook.com">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <style type="text/css" style="display:none;">P {margin-top:0;margin-bottom:0;}</style>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        Greetings community. </div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);"
        id="geom_inter_1630010826961_92_17">
        I am modelling a multizone building and I have two questions.</div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);"
        id="geom_inter_1630010826962_78_18">
        First, I would like to know if I am modelling the geometry
        correctly (through the TRNbuild wizard). It is a two floor
        apartment building with two apartments in each floor, so in the
        floorplan window, I model it as two separate floors (three zones
        each, with the middle zones representing the hallways)-as shown
        in the picture- and then connecting the floors  with adjacent
        floors ( or ceilings). Is that the right way ? </div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        Secondly, I am constantly running into problems with the air
        pump system I am using. I have tried both approaches -DOE
        coefficient and catalog data- type 966 and 954 respectively, but
        I cant seem to solve the warnings and errors of the simulation.
        Some common problems i get are: Error 118  (SAT subroutine was
        called with a temperature below absolute zero), fail of input
        convergence, controller (Type 166) sticks for a considerable
        amount of timesteps. I also experience a very slow simulation
        even with a timestep of 1 hour. I have tried many things like
        short timestep, calibrating the heat pumps capacity, increasing
        the zone's thermal capacitance, using the absolute instead of
        the relative humidity etc.  but when I manage to erase one
        problem the other appears.</div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        If anyone has some idea about what might be going wrong in my
        case I would be reaally grateful, considering the time I have
        consumed trying to get it right. I attached the .tpf of the
        simulation for better a understanding of my project. <span
          style="background-color:rgb(255, 255, 255);display:inline
          !important">Looking forward for your ideas.</span></div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        <span style="background-color:rgb(255, 255, 255);display:inline
          !important"><br>
        </span></div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        <span style="background-color:rgb(255, 255, 255);display:inline
          !important">Thanks in advance,</span></div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        <br>
      </div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        Jim Soukoulis</div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        National Technical University of Athens.</div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
         </div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>