<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html;
      charset=windows-1252">
  </head>
  <body>
    <p>Jim,</p>
    <p>  I am not sure to what extent you changed the time step but I am
      almost always using something between 1 and 5 minutes these days.
      If your heat pump is the right size for the space and you're using
      a 1 minute timestep already then you might send the project to
      your distributor in the hopes that they can give some guidance.</p>
    <p><br>
    </p>
    <p>  The heat pump data file out of range issue is not uncommon and
      if it isn't happening too much of the time then I wouldn't worry
      about it. The issue is that the routine that reads that data file
      can interpolate within the range covered by the data file but
      can't extrapolate beyond it. Instead, if a value comes in beyond
      the range, the routine will just find the closest value (at the
      bottom or top of the range given) and report that value. This can
      get you into some trouble; if your heat pump data file only goes
      down to an outdoor ambient temperature of 5C and yet during your
      simulation an outdoor ambient temperature of -20C is encountered
      then your heat pump will report the same available heating
      capacity at both 5 and -20C, which probably is not accurate. Again
      if it is only happening a few times per simulation it is nothing
      to worry about. If it is happening more then you can edit the data
      file to extend its range.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 08/18/2021 12:42, dimitris soukoulis
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:VI1PR08MB3503966A11F7AE0E30384DE6A7FE9@VI1PR08MB3503.eurprd08.prod.outlook.com">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <style type="text/css" style="display:none;">P {margin-top:0;margin-bottom:0;}</style>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        <meta content="text/html; charset=windows-1253">
        <meta name="ProgId" content="Word.Document">
        <meta name="Generator" content="Microsoft Word 15">
        <meta name="Originator" content="Microsoft Word 15">
      </div>
      <div class="WordSection1">
        <p class="MsoNormal" style="margin: 0cm; font-size: 11pt;
          font-family: "Calibri", sans-serif;">
          <span style="" lang="EN-US">Hello! I am modeling a multizone
            building air conditioning scenario using the type 954c air
            source heat pump. I keep getting two kind of warnings.
            <b>The first</b> is for the type 166 controller and says
            that the controller is stuck for some considerable amount of
            time (17 percent). I tried changing the heat pumps
            characteristics to fit the rooms needs better and also
            changed the timestep  but  I couldnt erase the warning. <b>The
              second warning </b>was for the heat pumps data file. It
            says that in the simulation the cooling performance data
            file was called several times with a first (and sometimes
            second and third) independent variable value below (or
            sometimes above) the range supplied in the data file. Does
            anybody have any ideas about how to fix those two problems ?
            Thanks in advance.</span></p>
        <p class="MsoNormal" style="margin: 0cm; font-size: 11pt;
          font-family: "Calibri", sans-serif;">
          <span style="" lang="EN-US">Jim Soukoulis.<br>
          </span></p>
        <p class="MsoNormal" style="margin: 0cm; font-size: 11pt;
          font-family: "Calibri", sans-serif;">
           </p>
        <p class="MsoNormal" style="margin: 0cm; font-size: 11pt;
          font-family: "Calibri", sans-serif;">
          <span style=""><br>
          </span></p>
        <span style=""></span>
        <p class="MsoNormal" style="margin: 0cm; font-size: 11pt;
          font-family: "Calibri", sans-serif;">
          <span style=""> </span></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>