<p>Sherif,</p>
<p> It is almost always possible to set such things up using
boolean operators in equations that you combine together. To write
the example conditional statement in your email you might do:<br>
</p>
isOcc = GT(occ,0.001)<br>
PPDsmall = LT(PPD,6)<br>
categoryA = AND(isOcc,PPDsmall)
<p>but of course you can combine them all into one equation if you
want:</p>
<p>categoryA = AND(GT(occ,0.001),LT(PPD,6)) <br>
</p>
<p>The result of the equations categoryA will be 1 if both of the
other conditions are met and 0 otherwise. You can then feed the
value of categoryA into an integrator to find out how much time
during the year your building was in that condition</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<p><br>
</p>
<p><br>
</p>
<div class="moz-cite-prefix">On 07/17/2021 03:44, SHERIF SAIED via
TRNSYS-users wrote:<br>
</div>
<blockquote type="cite"
cite="mid:CAJSajLaEfgV3rPLyNf0T-_RKP_gk82ocd4k=PkeEyL2mMtJctw@mail.gmail.com">
<meta http-equiv="content-type" content="text/html; charset=UTF-8">
<div dir="ltr"><img src="cid:part1.7CDBB4B6.E988F654@tess-inc.com"
alt="IMG-20210716-WA0042.jpg" class="" width="497" height="89"><br>
<div>I want to make like this table in trnsys using some
functions for greater than or smaller than in equator. for
example if PPD < 6 and signal of occ.=1 then count me the
hours for this condition on all year and so on ...How are
these equations to be like? and if I need to use a specific
type for getting this or just using the equator?</div>
<div>Regards,</div>
<div>Sherif</div>
<div dir="ltr" class="gmail_signature"
data-smartmail="gmail_signature">
<div dir="ltr">
<div>
<div dir="ltr"><b>Sherif Saied.</b>
<div><b>Tel: (</b>+2)01004419468 / (+2)01124348957</div>
<div><br>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>