    <p>Pouyan,</p>
    <p> The method I usually use when sizing equipment (radiators or
      otherwise) is to set each room of the building up with a set point
      temperature and an automatic heating type in TRNBuild. I then find
      the max hourly heating required from among the Type56 outputs and
      then size each piece of equipment accordingly. It sounds as though
      your method is the same.</p>
    <p> 10C sounds correct for a design air temperature but keep in mind
      that the radiator's capacity can be quite different if you are
      asking it to maintain an air temperature that is significantly
      different than the design air temperature. You may run into
      trouble if you set the design air temperature to 10C but are in
      fact trying to maintain 20C in the room.</p>
    <p> I unfortunately don't have any experience regarding setting the
      number of channels. However, I would encourage you to play around
      with the value. Make your best guess and run a simulation.
      Increase the number by 20% and run again. Decrease it by 20% and
      run it again. Look at the results each time and determine whether
      those results are sensitive to the value in question. If they are
      then you can dig in and try and get a more accurate value; perhaps
      by talking to manufacturers. If they aren't then you can proceed
      using your best guess value.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 07/14/2021 08:15, Pouyan
      Talebizadehsardari (Staff) via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:LO0P265MB48959D1E5A01E3816B8D8E8FCD139@LO0P265MB4895.GBRP265.PROD.OUTLOOK.COM">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style>@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}@font-face
        {font-family:DengXian;
        panose-1:2 1 6 0 3 1 1 1 1 1;}@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}@font-face
        {font-family:"\@DengXian";
        panose-1:2 1 6 0 3 1 1 1 1 1;}p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;
        mso-fareast-language:EN-US;}a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:#0563C1;
        text-decoration:underline;}a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri",sans-serif;
        color:windowtext;}.MsoChpDefault
        {mso-style-type:export-only;
        font-family:"Calibri",sans-serif;
        mso-fareast-language:EN-US;}div.WordSection1
        {page:WordSection1;}</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span style="font-size:12.0pt">Dear All,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt">I hope all
            are well. I’d really appreciate it if anyone can help me
            with the following questions:<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt">I am using a
            radiator (Type 1231) for each room to warm up a building
            (Type 56). First, I determined the maximum loss for this
            building by choosing a heating setpoint. Then, I chose the
            maximum heat loss for each room as the design capacity of
            the radiator. Does anyone know if I do it correct?<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt">I chose 55C
            for the design surface temperature of the radiator. My
            boiler works at the temperature of 60C. What about the
            design air temperature? As I know, these values are selected
            based on the manufacturer and it is usually 50C less than
            the mean temperature of the radiator. So, I consider it the
            predefined value of 10C.  Am I correct?
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt">Also, for
            the number of pipes,  as I understand, it is related to
            correct the heat transfer to the room and a higher number of
            pipes results in a lower heat transferred to the room. Does
            anyone know if it is exactly equal to the number of water
            channels insider the radiator? If yes, so, It should be
            related to the length of the radiator and so a higher number
            should be selected for a radiator with a higher capacity.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt">Thanks in
            advance<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt">Kind regards<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-size:12.0pt">Pouyan<o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal" style="background:white"><b><span
              style="color:#201F1E;border:none windowtext
              1.0pt;padding:0cm;mso-fareast-language:EN-GB">*******************************************************************************</span></b><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif;color:#222222;mso-fareast-language:EN-GB"><o:p></o:p></span></p>
        <p class="MsoNormal" style="background:white"><b><span
              style="font-size:12.0pt;font-family:"Times New
              Roman",serif;color:#201F1E;border:none windowtext
              1.0pt;padding:0cm;mso-fareast-language:EN-GB">Pouyan
              Talebizadeh Sardari</span></b><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif;color:#201F1E;border:none windowtext
            1.0pt;padding:0cm;mso-fareast-language:EN-GB">, BSc MSc PhD
            AFHEA</span><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif;color:#222222;mso-fareast-language:EN-GB"><o:p></o:p></span></p>
        <p class="MsoNormal" style="background:white"><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif;color:#201F1E;border:none windowtext
            1.0pt;padding:0cm;mso-fareast-language:EN-GB">Centre for
            Sustainable Energy Use in Food Chains,
            <o:p></o:p></span></p>
        <p class="MsoNormal" style="background:white"><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif;color:#201F1E;border:none windowtext
            1.0pt;padding:0cm;mso-fareast-language:EN-GB">Institute of
            Energy Futures,
            <o:p></o:p></span></p>
        <p class="MsoNormal" style="background:white"><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif;color:#201F1E;border:none windowtext
            1.0pt;padding:0cm;mso-fareast-language:EN-GB">Brunel
            University London,
            <o:p></o:p></span></p>
        <p class="MsoNormal" style="background:white"><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif;color:#201F1E;border:none windowtext
            1.0pt;padding:0cm;mso-fareast-language:EN-GB">Kingston Lane,
            Uxbridge, Middlesex, UB8 3PH, UK
          </span><span style="font-size:12.0pt;font-family:"Times
            New
            Roman",serif;color:#222222;mso-fareast-language:EN-GB"><o:p></o:p></span></p>
        <p class="MsoNormal" style="background:white"><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif;color:#201F1E;border:none windowtext
            1.0pt;padding:0cm;mso-fareast-language:EN-GB">Email: </span><span
            style="mso-fareast-language:EN-GB"><a
              href="mailto:pouyan.talebizadehsardari@brunel.ac.uk"
              moz-do-not-send="true"><span
                style="font-size:12.0pt;font-family:"Times New
                Roman",serif;color:blue;border:none windowtext
                1.0pt;padding:0cm">pouyan.talebizadehsardari@brunel.ac.uk</span></a></span><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif;color:#222222;mso-fareast-language:EN-GB"><o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>