<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
  </head>
  <body>
    <p>Sherif,</p>
    <p>  Using a differential controller will work but Trnsys18 also has
      some just-plain-thermostat models (Type106 or Type166) that might
      be easier to implement. You'll need two connections. One
      connection might come from an equation or a combination of an
      equation and a forcing function that results in the temperature
      that you want the boiler to supply. The equation might be:</p>
    isSummer = AND(GT(TIME,3624),LT(TIME,6552))<br>
    isWinter = 1-isSummer<br>
    boilerSetPoint = 85.*isSummer + 40.*isWinter
    <p>The other connection will be the temperature that is being
      monitored to decide whether the boiler should be on or off. Again
      you'll probably need some equations here so that the decision to
      turn on the boiler can come in summer when conditions are such
      that you want to run the chiller or in winter when you want heat.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <p>  <br>
    </p>
    <div class="moz-cite-prefix">On 07/08/2021 17:14, SHERIF SAIED via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAJSajLbGnnpm_DxjC=iO8fHfLZ1ao+mGGbu3GQ9o1NiSHbm=eA@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">checked Thanks, I have another question I used a
        differential controller to the boiler type 700 and need
        temperature out of it in the range between 80-90 in
        summer(cooling season) to supply absorption chiller and need
        temperature in winter(heating season) in the range of 30-45. I
        linked the upper input Temp.(Th) to outlet of the boiler, linked
        the lower input Temp.(TL) to the return flow from the tank to
        the boiler. for monitoring Temp. (Tin),upper dead band(dt) and
        lower dead band(dt) I don't really know how to link or what
        value should be. could anyone help, please?, Thanks in advance.</div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Tue, Jul 6, 2021 at 8:32 PM
          David BRADLEY <<a href="mailto:d.bradley@tess-inc.com"
            moz-do-not-send="true">d.bradley@tess-inc.com</a>> wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0px 0px 0px
          0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div>
            <p>Sherif,</p>
            <p>  There are a number of examples in the
              .\Trnsys18\Examples\HVACTemplates\ folder that will give
              you some ideas about how to implement control of HVAC
              systems. Have a look at the 10-Examples.pdf documentation
              in parallel with those examples. I don't think that any of
              them have a radiant floor in them but the principals are
              the same. <br>
            </p>
            <p>You might also have a look at the example:<br>
            </p>
            <p>.\Trnsys18\Examples\Feedback Control\SunSpace - Floor
              heating PID controller.tpf</p>
            <p>Its controls are possibly more complicated than the ones
              in your case but it will show how to do the system-level
              connections between Type56's active layers and the HVAC
              system.</p>
            <p>kind regards,</p>
            <p> David</p>
            <p><br>
            </p>
            <p><br>
            </p>
            <div>On 07/06/2021 10:20, SHERIF SAIED via TRNSYS-users
              wrote:<br>
            </div>
            <blockquote type="cite">
              <div dir="ltr">Hello everyone,
                <div><br>
                </div>
                <div>I need help in some controls on radiant cooling and
                  heating system model like type 165 to control either
                  boiler for heating system or control building
                  temperatures, also need to control on different
                  components for the cooling system to work uniformly
                  according to season if summer cooling system work and
                  if winter will work the heating system and so on . I
                  have problems in PPD and PMV for building through all
                  year. if anyone would help or have an example model
                  for how I can set these controllers in two systems?</div>
                <div>Regards, <br>
                  -- <br>
                  <div dir="ltr">
                    <div dir="ltr">
                      <div>
                        <div dir="ltr"><b>Sherif Saied.</b>
                          <div><b>Tel: (</b>+2)01004419468 /
                            (+2)01124348957</div>
                          <div><br>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
              <br>
              <fieldset></fieldset>
              <pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank" moz-do-not-send="true">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
            </blockquote>
            <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a href="mailto:d.bradley@tess-inc.com" target="_blank" moz-do-not-send="true">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank" moz-do-not-send="true">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank" moz-do-not-send="true">http://www.trnsys.com</a></pre>
          </div>
        </blockquote>
      </div>
      <br clear="all">
      <div><br>
      </div>
      -- <br>
      <div dir="ltr" class="gmail_signature">
        <div dir="ltr">
          <div>
            <div dir="ltr"><b>Sherif Saied.</b>
              <div><b>Tel: (</b>+2)01004419468 / (+2)01124348957</div>
              <div><br>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>