    <p>Adnan,</p>
    <p> If the flow rate is proportional to the ambient temperature then
      there are some models in the TESS Controls library that you can
      use (Type1250 for example). If you are doing feedback control (in
      other words comparing a temperature to a desired temperature and
      implementing a controller whose signal is proportional to the
      difference between the two as well as to the integral of the
      error) then there are some model in the standard controls library.
      You might look at Types 22 and 23. PI and PID control can be a
      little tricky in TRNSYS because we discretize time into time steps
      that are quite long in comparison to the rate at which true PID
      control samples and adjusts a control signal. I would recommend
      looking at the PID example and documentation for some hints on how
      to set it up.<br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 06/17/2021 21:17, adnan rasheed via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAG9tXZi4fbMpzC52vh3e87ixtTGcP8G+Tgd2B=Nej9RNtMKCZw@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr"><br clear="all">
        <div>Hi everyone,</div>
        <div><br>
        </div>
        <div>I am using a hot water storage tank in which hot water is
          coming from the heat pump. From the hot water storage tank to
          building flow rate was controlled by PI controller in
          experiment giving some p and i values. The system works in
          this way: when more heating is needed and
          outside temperature goes down, more flow and less heating
          needs less flow coming from the storage tank . I am confused
          which controller I should use in this situation? or do I need
          to write an equation??</div>
        <div><br>
        </div>
        <div>Thanks </div>
        <div> </div>
        -- <br>
        <div dir="ltr" class="gmail_signature"
          data-smartmail="gmail_signature">
          <div dir="ltr">
            <div dir="ltr">
              <div dir="ltr"><font face="georgia, serif" color="#666666">Adnan </font></div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>