    <p><span style="mso-fareast-language:ES">José Javier,</span></p>
    <p><span style="mso-fareast-language:ES"> I would put a Type65 on
        the cooling coil to see the inlet and outlet temperatures and
        flowrates on both the air and water sides as the simulation
        progresses. I think you may find that the inlet liquid
        temperature may not always be coming in as cold as you need it
        to in order to bring the air temperature down as far as 2.8C. <br>
      </span></p>
    <p><span style="mso-fareast-language:ES"> Also make sure that there
        is some thermal capacitance in the liquid loop. If you have just
        the cooling coil, a pump, and a chiller (or whatever device is
        providing the cold liquid) then you'll want to add pipes and/or
        a tank so that the loop is numerically stable as so as to more
        accurately model the transient impact of the loop heating up and
        cooling down as a function of time (rather than instantaneously
        because you are only using quasi steady state models)</span></p>
    <p><span style="mso-fareast-language:ES">kind regards,</span></p>
    <p><span style="mso-fareast-language:ES"> David</span></p>
    <p><span style="mso-fareast-language:ES"><br>
      </span></p>
    <div class="moz-cite-prefix">On 06/15/2021 09:28, RUBIO RUBIO, JOSÉ
      JAVIER via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:DB6PR0801MB19110E8CEEEB2CCBBF46AC1FD7309@DB6PR0801MB1911.eurprd08.prod.outlook.com">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style>@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;
        mso-fareast-language:EN-US;}.MsoChpDefault
        {mso-style-type:export-only;
        font-family:"Calibri",sans-serif;
        mso-fareast-language:EN-US;}div.WordSection1
        {page:WordSection1;}</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal">Dear all,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span lang="EN-GB">I am using the Type 508
            to model a cooling coil with the outlet air temperature set
            to a constant value. As far as I am concerned, there is
            enough air flowrate as well as fluid flowrate during the
            simulation but the outlet air temperature is much higher
            than the setpoint (for example, the setpoint is 2.8 ºC and
            the outlet air temperature is 12 ºC). Anyone can help me to
            understand why is that?<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-GB"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="mso-fareast-language:ES"
            lang="EN-GB">Thanks in advance,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="mso-fareast-language:ES"
            lang="EN-GB"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="mso-fareast-language:ES"
            lang="EN-GB">Regards,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="mso-fareast-language:ES"
            lang="EN-GB"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="mso-fareast-language:ES">José
            Javier Rubio Rubio.<o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>