<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
  </head>
  <body>
    <p>Ashmin,</p>
    <p> The controller can make one control decision per time step. When
      the controller decides to turn on the cooling equipment then the
      cooling equipment has to stay on for 5 minutes, driving the
      temperature of the space downwards, perhaps beyond the limit of
      the dead band. If you use a 1 minute timestep instead then the
      controller has a chance every minute to turn the cooling equipment
      back off, limiting the temperature overshoot in the building.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 05/25/2021 08:01, asmin aryal wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAAynMJw8wTe=QBRkDbrOC4AUqcmVsPMa22KwZwO8ZbzvPFS7SQ@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">Dear Sir,
        <div>I am cooling type 56 building with type  type 752 (Simple
          Cooling Coil Using Bypass Fraction Approach; Temperature
          Controlled) by introducing the cool air via ventilation to
          type 56.</div>
        <div> I am controlling the room air temperature by type 2:
          aquastatC controller. When i run the simulation with 5 min
          time step, the controller cannot control the room air
          temperature within the dead band but when i run the simulation
          with 1 min time step it can control the room temperature
          within the dead band.</div>
        <div>What may be the possible reason.  </div>
        <div>Looking forward to your answer.</div>
        <div><img src="cid:part1.3CA4BDB2.D70F220F@tess-inc.com"
            alt="image.png" style="margin-right: 0px;" class=""
            width="470" height="380"><br>
        </div>
        <div><br>
        </div>
        <div><img src="cid:part2.2DB2F84E.E1D859A0@tess-inc.com"
            alt="image.png" style="margin-right: 0px;" class=""
            width="470" height="239"><br>
        </div>
        <div>Sincerely </div>
        <div>Ashmin Aryal </div>
      </div>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>