    <p><span lang="EN-CA">Michaël</span> and Marion,</p>
    <p>  Might it be possible for that diagram to work its way (with a
      nice big reference to the generosity of its author of course!!)
      into the Type56 manual? We get this question a lot on the
      hotlines.</p>
    <p>db<br>
    </p>
    <div class="moz-cite-prefix">On 04/12/2021 05:11, hotline via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:AM6PR01MB4884EEC820A2F32EA30D974BBA709@AM6PR01MB4884.eurprd01.prod.exchangelabs.com">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style>@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}@font-face
        {font-family:Garamond;
        panose-1:2 2 4 4 3 3 1 1 8 3;}p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;
        mso-fareast-language:EN-US;}a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}pre
        {mso-style-priority:99;
        mso-style-link:"HTML Vorformatiert Zchn";
        margin:0cm;
        font-size:10.0pt;
        font-family:"Courier New";
        mso-fareast-language:EN-GB;}span.HTMLVorformatiertZchn
        {mso-style-name:"HTML Vorformatiert Zchn";
        mso-style-priority:99;
        mso-style-link:"HTML Vorformatiert";
        font-family:Consolas;
        mso-fareast-language:EN-US;}span.E-MailFormatvorlage26
        {mso-style-type:personal-compose;
        font-family:"Calibri",sans-serif;
        color:windowtext;}.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}div.WordSection1
        {page:WordSection1;}</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span lang="EN-CA">Michaël</span>,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span lang="EN-US">your overview  explains
            the balance of an external opaque surface very well.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">The only “missing”
            feature is the surface gain on the “outside face”.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">This gain is included in
            QABSO (NTYPE 22 ). Therefore, QABSO isn’t  “short wave
            radiation” only if a surface gain on the “outside face” is
            defined.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Marion<o:p></o:p></span></p>
        <div>
          <p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#A6A6A6;mso-fareast-language:DE"
              lang="EN-US"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#A6A6A6;mso-fareast-language:DE"
              lang="EN-US"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#A6A6A6;mso-fareast-language:DE">Transsolar
              Energietechnik GmbH | Curiestrasse 2 | 70563 Stuttgart |
              Germany<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#A6A6A6;mso-fareast-language:DE">CEO:
              Matthias Schuler, Thomas Auer, Stefan Holst, Dieter
              Schnelle
              <o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#A6A6A6;mso-fareast-language:DE">Registered
              at Amtsgericht Stuttgart HRB 23347 | USt-IdNr.: DE
              152272639<o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0cm 0cm 0cm">
            <p class="MsoNormal"><b><span
                  style="mso-fareast-language:DE">Von:</span></b><span
                style="mso-fareast-language:DE"> TRNSYS-users
                <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-bounces@lists.onebuilding.org"><trnsys-users-bounces@lists.onebuilding.org></a>
                <b>Im Auftrag von </b>Michaël Kummert via TRNSYS-users<br>
                <b>Gesendet:</b> Samstag, 10. April 2021 19:04<br>
                <b>An:</b> 'TRNSYS users mailing list at
                OneBuilding.org'
                <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@lists.onebuilding.org"><trnsys-users@lists.onebuilding.org></a><br>
                <b>Cc:</b> Michaël Kummert
                <a class="moz-txt-link-rfc2396E" href="mailto:michael.kummert@gmail.com"><michael.kummert@gmail.com></a><br>
                <b>Betreff:</b> Re: [TRNSYS-users] FW: Net radiation
                received on a specific internal surface - Type 56<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span lang="EN-CA">Kan,<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-CA"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-CA">I struggled with those
            Type 56 outputs recently and I came up with the attached
            interpretation.
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-CA">I hope this helps, and I
            hope someone from Transsolar will correct me if I
            misinterpreted some outputs.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-CA"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-CA">Michaël Kummert<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-CA">Polytechnique Montréal<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-CA"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0cm 0cm 0cm">
            <p class="MsoNormal"><b><span
                  style="mso-fareast-language:EN-CA" lang="EN-US">From:</span></b><span
                style="mso-fareast-language:EN-CA" lang="EN-US">
                TRNSYS-users <<a
                  href="mailto:trnsys-users-bounces@lists.onebuilding.org"
                  moz-do-not-send="true">trnsys-users-bounces@lists.onebuilding.org</a>>
                <b>On Behalf Of </b>K.R. Gunawardena via TRNSYS-users<br>
                <b>Sent:</b> April 9, 2021 10:44<br>
                <b>To:</b> David BRADLEY <<a
                  href="mailto:d.bradley@tess-inc.com"
                  moz-do-not-send="true">d.bradley@tess-inc.com</a>>;
                TRNSYS users mailing list at OneBuilding.org <<a
                  href="mailto:trnsys-users@lists.onebuilding.org"
                  moz-do-not-send="true">trnsys-users@lists.onebuilding.org</a>><br>
                <b>Cc:</b> K.R. Gunawardena <<a
                  href="mailto:krag2@cam.ac.uk" moz-do-not-send="true">krag2@cam.ac.uk</a>><br>
                <b>Subject:</b> Re: [TRNSYS-users] FW: Net radiation
                received on a specific internal surface - Type 56<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><span lang="EN-CA"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-family:"Garamond",serif" lang="EN-GB">Many
            thanks David for your response and clarification!<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-family:"Garamond",serif" lang="EN-GB"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-family:"Garamond",serif" lang="EN-GB">QIBAB
            and QIDAB would address shortwave absorption. What about the
            longwave exchange?<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-family:"Garamond",serif" lang="EN-GB"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-family:"Garamond",serif" lang="EN-GB">I
            am currently working under the following assumptions:
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-family:"Garamond",serif" lang="EN-GB"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-family:"Garamond",serif" lang="EN-GB">To
            get the radiative gains for the internal/indoor wall’s
            surface  =  radiative airnode internal gains received by
            wall (assumed to be given by QRGAB)  +  solar gains through
            zone windows received by walls ( assumed as QIBAB + QIDAB or
            QSIAB as a total?)  +  longwave radiation exchange between
            this wall and all other walls and windows (QABSILW? not sure
            about this one).<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-family:"Garamond",serif" lang="EN-GB"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-family:"Garamond",serif" lang="EN-GB">Your
            clarification is greatly appreciated!<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-family:"Garamond",serif" lang="EN-GB"><o:p> </o:p></span></p>
        <p class="MsoNormal"><b><span
              style="font-family:"Garamond",serif"
              lang="EN-GB">Best regrads,<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-family:"Garamond",serif"
              lang="EN-GB">Kan
              <o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-family:"Garamond",serif"
              lang="EN-GB"><o:p> </o:p></span></b></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0cm 0cm 0cm">
            <p class="MsoNormal"><b><span
                  style="mso-fareast-language:EN-GB" lang="EN-US">From:</span></b><span
                style="mso-fareast-language:EN-GB" lang="EN-US"> David
                BRADLEY <<a href="mailto:d.bradley@tess-inc.com"
                  moz-do-not-send="true">d.bradley@tess-inc.com</a>>
                <br>
                <b>Sent:</b> 09 April 2021 15:12<br>
                <b>To:</b> TRNSYS users mailing list at OneBuilding.org
                <<a href="mailto:trnsys-users@lists.onebuilding.org"
                  moz-do-not-send="true">trnsys-users@lists.onebuilding.org</a>><br>
                <b>Cc:</b> K.R. Gunawardena <<a
                  href="mailto:krag2@cam.ac.uk" moz-do-not-send="true">krag2@cam.ac.uk</a>><br>
                <b>Subject:</b> Re: [TRNSYS-users] FW: Net radiation
                received on a specific internal surface - Type 56<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><span lang="EN-GB"><o:p> </o:p></span></p>
        <p><span lang="EN-GB">Kan,</span><span
            style="mso-fareast-language:EN-GB" lang="EN-GB"><o:p></o:p></span></p>
        <p><span lang="EN-GB">  I often use QIBAB and QIDAB (NTypes 80
            and 81). Those are the quantities of radiation absorbed (as
            opposed to incident) on the inside surface, however.<o:p></o:p></span></p>
        <p><span lang="EN-GB">  Wall gains are specified as totals, not
            per square metre.<o:p></o:p></span></p>
        <p><span lang="EN-GB">kind regards,<o:p></o:p></span></p>
        <p><span lang="EN-GB"> David<o:p></o:p></span></p>
        <p><span lang="EN-GB"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><span lang="EN-GB">On 04/09/2021 05:15,
              K.R. Gunawardena via TRNSYS-users wrote:<o:p></o:p></span></p>
        </div>
        <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
          <p class="MsoNormal"><span
              style="font-family:"Garamond",serif"
              lang="EN-GB">Hi,</span><span lang="EN-GB"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-family:"Garamond",serif"
              lang="EN-GB"> </span><span lang="EN-GB"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-family:"Garamond",serif"
              lang="EN-GB">I am trying to get clarification on a couple
              of issues.</span><span lang="EN-GB"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-family:"Garamond",serif"
              lang="EN-GB"> </span><span lang="EN-GB"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-family:"Garamond",serif"
              lang="EN-GB">I am trying to couple a bespoke component
              with Type 56 to calculate surface evaporative flux. I want
              to input the net radiation received on a specific internal
              surface as an input to this component. Which trnsys output
              best represents the net radiation energy received by an
              internal surface?
            </span><span lang="EN-GB"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-family:"Garamond",serif"
              lang="EN-GB"> </span><span lang="EN-GB"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-family:"Garamond",serif"
              lang="EN-GB">Second, when specifying a wall gain, do we
              provide the value for the entire wall or m^2?</span><span
              lang="EN-GB"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-family:"Garamond",serif"
              lang="EN-GB"> </span><span lang="EN-GB"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-family:"Garamond",serif"
              lang="EN-GB">Answers are greatly appreciated,</span><span
              lang="EN-GB"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-family:"Garamond",serif"
              lang="EN-GB">Best regards,</span><span lang="EN-GB"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-family:"Garamond",serif"
              lang="EN-GB">Kan </span>
            <span lang="EN-GB"><o:p></o:p></span></p>
          <p class="MsoNormal" style="margin-bottom:12.0pt"><span
              style="mso-fareast-language:EN-GB" lang="EN-GB"><o:p> </o:p></span></p>
          <pre><span lang="EN-GB">_______________________________________________<o:p></o:p></span></pre>
          <pre><span lang="EN-GB">TRNSYS-users mailing list<o:p></o:p></span></pre>
          <pre><span lang="EN-GB"><a href="mailto:TRNSYS-users@lists.onebuilding.org" moz-do-not-send="true">TRNSYS-users@lists.onebuilding.org</a><o:p></o:p></span></pre>
          <pre><span lang="EN-GB"><a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><o:p></o:p></span></pre>
        </blockquote>
        <pre><span lang="EN-GB">-- <o:p></o:p></span></pre>
        <pre><span lang="EN-GB">***************************<o:p></o:p></span></pre>
        <pre><span lang="EN-GB">David BRADLEY<o:p></o:p></span></pre>
        <pre><span lang="EN-GB">Principal<o:p></o:p></span></pre>
        <pre><span lang="EN-GB">Thermal Energy Systems Specialists, LLC<o:p></o:p></span></pre>
        <pre><span lang="EN-GB">3 North Pinckney Street - suite 202<o:p></o:p></span></pre>
        <pre><span lang="EN-GB">Madison, WI  53703 USA<o:p></o:p></span></pre>
        <pre><span lang="EN-GB"><o:p> </o:p></span></pre>
        <pre><span lang="EN-GB">P:+1.608.274.2577<o:p></o:p></span></pre>
        <pre><span lang="EN-GB"><a href="mailto:d.bradley@tess-inc.com" moz-do-not-send="true">d.bradley@tess-inc.com</a><o:p></o:p></span></pre>
        <pre><span lang="EN-GB"><o:p> </o:p></span></pre>
        <pre><span lang="EN-GB"><a href="http://www.tess-inc.com" moz-do-not-send="true">http://www.tess-inc.com</a><o:p></o:p></span></pre>
        <pre><span lang="EN-GB"><a href="http://www.trnsys.com" moz-do-not-send="true">http://www.trnsys.com</a><o:p></o:p></span></pre>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>