    <p>Luís,</p>
    <p>  I would definitely suggest putting in a storage tank. One thing
      you can do is to have the heat pumps feed hot water to the storage
      tank and have the radiant floor and radiators draw as needed from
      the storage tank. In the real world (not just in the simulation)
      the heat pumps will struggle during times when there is little
      need for heat because their capacity is fairly fixed (assuming
      they are constant speed compressor devices) and when there is
      little load, the hot water that they produce will circulate
      through the system and return to the heat pump with only a small
      drop in temperature. Heat pumps don't like their return
      temperature to get too high and they shut themselves off if it
      does. I learned that the hard way in an actual building after not
      believing what TRNSYS was telling me!!   <br>
    </p>
    <p>  As for the heat pump data file, if you have access to the TESS
      HVAC library you will find heat pumps that use a normalized data
      file meaning that they can be resized by adjusting a few
      parameters rather than by recreating the data file.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 03/24/2021 12:10, Luis Santos via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CALhB1ENpHszhNZc1p+fKMKhT+WtzE1SgYFqRP-EMSwASTDcBNQ@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">Hello, 
        <div><br>
        </div>
        <div>I´m new to the software TRNSYS and I´m still confused about
          how many and which components do I need for my simulations.</div>
        <div>The site is located in Cork (Ireland) and its present
          heating system relies on a gas-fired boiler. For my master
          thesis I need to simulate the performance of the boiler
          itself, a geothermal heat pump (both connected to radiators)
          and at last the GSHP connected to a theoretical underfloor
          heating. I don´t have any informations about the piping system
          nor the circulating pumps, and I´m wondering if I need a
          storage tank. A central heating (church) needs a tank, or can
          the water be transferred directly to the radiators?</div>
        <div>I want to use a water-to-water heat pump
          (geothermal/vertical) to heat a church with radiators. Since
          the climate doesn´t require any cooling, the heat pump should
          only be applied for heating purposes. After one chooses a heat
          pump of a certain manufacturer, do we need to insert the
          values manually in the external files? I´ve seen examples
          where there are more than 500 lines in Excel, is there an
          easier way to do this?</div>
        <div><br>
        </div>
        <div>I´m sorry for the long and complicated text. Thank you in
          advance</div>
        <div><br>
        </div>
        <div>Luís </div>
        <div>Master in Thermal Energy </div>
        <div>FEUP</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>