<p>Are you dividing your flow by a simple fraction (80% goes to the
boiler and 20% goes to recirculation for example) or is the Type11
set up so that it tries to maintain a set point temperature like a
tempering valve might do? The error that you are getting is one
that comes when Type11 is used as a tempering valve but can't
achieve the set point because both of the inlet temperatures are
already above the set point. A little additional explanation might
help me find a suggestion for how to work around the issue.<br>
</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<div class="moz-cite-prefix">On 12/18/2020 08:02, Filippo Angeli via
TRNSYS-users wrote:<br>
</div>
<blockquote type="cite"
cite="mid:1618744424.3439293.1608300129039@mail.yahoo.com">
<meta http-equiv="content-type" content="text/html; charset=UTF-8">
<div class="yahoo-style-wrap" style="font-family:Helvetica Neue,
Helvetica, Arial, sans-serif;font-size:13px;">
<div dir="ltr" data-setdir="false">
<div>
<div dir="ltr" data-setdir="false">Good morning,</div>
<div>simulating the operation of a condensing boiler with a
power of 20kW and a setpoint temperature of 50 degrees; I
get the following error, which I report later, in type
11b. With this type I divide my flow rate into the boiler
flow rate and the recirculation flow rate.</div>
<div>"The inlet temperature and the heat source temperature
have simultaneously exceeded the set point temperature.
Gamma has been set to 0 (Mode 4) or 1 (Mode 5)."</div>
<div>I would like to have your help. Thanks.</div>
<div><br>
</div>
<div dir="ltr" data-setdir="false">Angeli Filippo</div>
</div>
<br>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>