<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
  </head>
  <body>
    <p>Dr Bina,</p>
    <p>  I would guess that the cause of the error is that the cooling
      data file doesn't have the correct number of data values in it or
      else that it does not exist where it is expected to be found. The
      file is not accessed until it is needed so it makes sense that the
      error would not appear until cooling is required in the building.
      <br>
    </p>
    <p>In "supply air conditioning" you want to select "external by
      another component" and then select "userdefined" for both the
      temperature and the humidity. Define input variables for each of
      these. When you save your changes in TRNBuild and return to the
      Studio you will have three new inputs (mass flow rate,
      temperature, and relative humidity) for the air that is going into
      that zone of the building. These will be passed from the fan coil
      model.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 11/08/2020 03:15, saeid
      mohammadzadeh via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CABCqxA+AcJks5oLBNS4WsiPQVgyOhbQz+A7EtG26Zn+VTjg5_A@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">Dear users;<br
            clear="all">
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">I
          have modeled a water-to-water heat pump which is connected to
          a fan coil (type 600). The fan coil is connected to a building
          (Type 56).</div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">for
          connection, I defined input as ventilation. When the system
          shifts to cooling mode, the system gives an error and stops
          suddenly. </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">I
          have another question regarding the ventilation inputs for fan
          coil:</div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">In
          "supply air conditioning" fan coil is an "external by other
          component" or internal calculation? </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
        </div>
        <div>
          <div dir="ltr" class="gmail_signature"
            data-smartmail="gmail_signature">
            <div dir="ltr">
              <div>
                <div dir="ltr">
                  <div dir="ltr">
                    <div dir="ltr">
                      <div dir="ltr">
                        <div dir="ltr">
                          <div dir="ltr">
                            <div dir="ltr">
                              <div dir="ltr">
                                <div dir="ltr">
                                  <div dir="ltr">
                                    <div dir="ltr">
                                      <div dir="ltr">
                                        <div dir="ltr">
                                          <div dir="ltr">
                                            <div dir="ltr">
                                              <div dir="ltr">
                                                <div
                                                  style="color:rgb(0,0,0)"><i
style="font-size:12.8px"><font size="2" color="#000000"><i><font
                                                          face="arial,
                                                          helvetica,
                                                          sans-serif"
                                                          color="#000000">Best
                                                          Regards</font></i></font></i><br>
                                                </div>
                                                <div
                                                  style="color:rgb(0,0,0)"><i><font
                                                      size="2"
                                                      face="arial,
                                                      helvetica,
                                                      sans-serif">Saeid
                                                      Mohammadzadeh
                                                      Bina, Dr. (Eng.)</font></i></div>
                                                <div
                                                  style="color:rgb(0,0,0)"><i
style="font-size:12.8px;color:rgb(34,34,34)"><font size="2" face="times
                                                      new roman, new
                                                      york, times,
                                                      serif"
                                                      color="#000000"><i><font
                                                          size="3"
                                                          face="arial,
                                                          helvetica,
                                                          sans-serif"
                                                          color="#000000">-------------------------------------------------</font></i></font></i></div>
                                                <div
                                                  style="color:rgb(0,0,0);font-family:HelveticaNeue,"Helvetica
Neue",Helvetica,Arial,"Lucida Grande",sans-serif"><font
                                                    size="2" face="times
                                                    new roman, new york,
                                                    times, serif"
                                                    color="#000000">
                                                    <div align="left"><font
style="font-size:16px" size="3" face="arial, helvetica, sans-serif"><font
                                                          size="2"
                                                          face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000">
                                                          <div
                                                          align="left"><em><font
                                                          face="times
                                                          new
                                                          roman,serif">Akita
                                                          <var></var>University</font></em><br>
                                                          </div>
                                                        </font></font><font
                                                        face="arial,
                                                        helvetica,
                                                        sans-serif"><font
                                                          size="2"
                                                          face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000">
                                                          <div
                                                          align="left"><span
style="font-family:"Times New Roman",serif"><i>Graduate
                                                          school of
                                                          International
                                                          Resource
                                                          Sciences</i></span><font
                                                          face="times
                                                          new
                                                          roman,serif"><em>.<br>
                                                          1-1 Tegata
                                                          gakuen-machi,
                                                          Akita
                                                          010-8502,
                                                          Japan</em></font></div>
                                                          <div
                                                          align="left"><font
                                                          face="times
                                                          new
                                                          roman,serif"><em>Tel: </em></font><em
style="font-family:"times new roman",serif">+815068665026
                                                          (Japan)</em></div>
                                                          <div
                                                          align="left"><em
style="font-family:"times new roman",serif">     
                                                           +989141011757
                                                          (Iran)</em><em
style="font-family:"times new roman",serif">   </em></div>
                                                        </font></font></div>
                                                    <div align="left"><font
style="font-size:16px" size="3" face="garamond, new york, times, serif"><em>E-mail: </em></font><a
href="mailto:s.mohammadzadeh66@gmail.com" target="_blank"
                                                        moz-do-not-send="true"><em>d9515254@s.akita-u.ac.jp</em></a><em
style="font-size:16px"> </em></div>
                                                    <div
                                                      style="font-size:16px"
                                                      align="left"><em
                                                        style="font-family:garamond,"new
york",times,serif;font-size:medium;background-color:rgba(0,0,0,0);margin:0px;padding:0px;color:blue"> 
                                                                 <a
                                                          href="mailto:mohammadzadehsaeid@yahoo.com"
                                                          rel="nofollow"
style="font-family:garamond,"new
york",times,serif;font-size:medium;background-color:rgba(0,0,0,0);margin:0px;padding:0px;color:blue"
target="_blank" moz-do-not-send="true">mohammadzadehsaeid@yahoo.com</a></em></div>
                                                  </font><font
                                                    style="font-size:16px"
                                                    size="2" face="times
                                                    new roman, new york,
                                                    times, serif"
                                                    color="#000000">
                                                    <div align="left">
                                                      <div
                                                        style="font-family:HelveticaNeue,"Helvetica
Neue",Helvetica,Arial,"Lucida
                                                        Grande",sans-serif;font-size:16px"><i><font
                                                          size="2"
                                                          face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000"><i><font
                                                          size="3"
                                                          face="arial,
                                                          helvetica,
                                                          sans-serif"
                                                          color="#000000">-------------------------------------------------<br>
                                                          <br>
                                                          </font></i></font></i></div>
                                                    </div>
                                                  </font></div>
                                              </div>
                                            </div>
                                          </div>
                                        </div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>