<p><I am simulating a large scale solar collector field. Now Im about to size the pump in the solar circuit. What is the correct approach? The inputs in the theoretical model does not consider pressure drops for example. Lets say if I have 500 collectors, can I assume that everyone is in parallell and multiply 500 with a nominal collector flow to get the pump size? Is that reasonable?></p>
<p>Erik - you would size the pump in TRNSYS like you would size it for a real world project.  You would need to calculate the pressure drop through the circuit at the flow rate you would like to maintain then find a pump that delivers the performance that you want.  Then simply take the pump information you need into TRNSYS; max flow rate, power at rated conditions, efficiency etc.</p>
<p>That's the best approach.  But since TRNSYS doesn't consider the pressure impacts, you can set whatever flow rate, efficiency, power that you want - even if it's not all that reasonable...</p>
<p>Are you allowing the pump to run at variable speed or only constant speed?</p>
<p> </p>
<p>Jeff</p>
<p> </p>
<div>
<pre>---<br />Jeff Thornton
President - TESS LLC
3 N. Pinckney Street, Suite 202, Madison WI USA 53703
Office: (608) 274-2577  Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton@tess-inc.com
</pre>
</div>
<p>On 08/16/2020 11:42 am, Erik Eriksson via TRNSYS-users wrote:</p>
<blockquote type="cite" style="padding-left:5px; border-left:#1010ff 2px solid; margin-left:5px"><!-- html ignored --><!-- head ignored --><!-- meta ignored --><!-- meta ignored -->
<div class="WordSection1">
<p class="MsoNormal">Hi!</p>
<p class="MsoNormal"><!-- o ignored --> </p>
<p class="MsoNormal">I am simulating a large scale solar collector field. Now Im about to size the pump in the solar circuit. What is the correct approach? The inputs in the theoretical model does not consider pressure drops for example. Lets say if I have 500 collectors, can I assume that everyone is in parallell and multiply 500 with a nominal collector flow to get the pump size? Is that reasonable?</p>
<p class="MsoNormal"><!-- o ignored --> </p>
<p class="MsoNormal"><!-- o ignored --> </p>
<p class="MsoNormal"><!-- o ignored --> </p>
<p class="MsoNormal">Best regards Erik<!-- o ignored --></p>
<p class="MsoNormal"><!-- o ignored --> </p>
</div>
<!-- html ignored --><br />
<pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
</body></html>