<div dir="ltr"><div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">Dear Dr. David;</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">I think my case is the second one that pops up in the online plotter and stops running. I will send my project tomorrow from my office with explanation about it. The first case is also interesting and I need to learn it (as I did not get it completely) for future works.</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small"><br></div><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div style="color:rgb(0,0,0)"><i style="font-size:12.8px"><font color="#000000" size="2"><i><font color="#000000" face="arial, helvetica, sans-serif">Best Regards</font></i></font></i><br></div><div style="color:rgb(0,0,0)"><i><font size="2" face="arial, helvetica, sans-serif">Saeid Mohammadzadeh Bina, Dr. (Eng.)</font></i></div><div style="color:rgb(0,0,0)"><i style="font-size:12.8px;color:rgb(34,34,34)"><font color="#000000" face="times new roman, new york, times, serif" size="2"><i><font color="#000000" face="arial, helvetica, sans-serif" size="3">-------------------------------------------------</font></i></font></i></div><div style="color:rgb(0,0,0);font-family:HelveticaNeue,"Helvetica Neue",Helvetica,Arial,"Lucida Grande",sans-serif"><font color="#000000" face="times new roman, new york, times, serif" size="2"><div align="left"><font face="arial, helvetica, sans-serif" size="3" style="font-size:16px"><font color="#000000" face="times new roman, new york, times, serif" size="2"><div align="left"><em><font face="times new roman,serif">Akita <var></var>University</font></em><br></div></font></font><font face="arial, helvetica, sans-serif"><font color="#000000" face="times new roman, new york, times, serif" size="2"><div align="left"><span style="font-family:"Times New Roman",serif"><i>Graduate
school of International Resource Sciences</i></span><font face="times new roman,serif"><em>.<br>1-1 Tegata gakuen-machi, Akita 010-8502, Japan</em></font></div><div align="left"><font face="times new roman,serif"><em>Tel: </em></font><em style="font-family:"times new roman",serif">+815068665026 (Japan)</em></div><div align="left"><em style="font-family:"times new roman",serif">       +989141011757 (Iran)</em><em style="font-family:"times new roman",serif">   </em></div></font></font></div><div align="left"><font face="garamond, new york, times, serif" size="3" style="font-size:16px"><em>E-mail: </em></font><a href="mailto:s.mohammadzadeh66@gmail.com" target="_blank"><em>d9515254@s.akita-u.ac.jp</em></a><em style="font-size:16px"> </em></div><div align="left" style="font-size:16px"><em style="font-family:garamond,"new york",times,serif;font-size:medium;background-color:rgba(0,0,0,0);margin:0px;padding:0px;color:blue">           <a href="mailto:mohammadzadehsaeid@yahoo.com" rel="nofollow" style="font-family:garamond,"new york",times,serif;font-size:medium;background-color:rgba(0,0,0,0);margin:0px;padding:0px;color:blue" target="_blank">mohammadzadehsaeid@yahoo.com</a></em></div></font><font color="#000000" face="times new roman, new york, times, serif" size="2" style="font-size:16px"><div align="left"><div style="font-family:HelveticaNeue,"Helvetica Neue",Helvetica,Arial,"Lucida Grande",sans-serif;font-size:16px"><i><font color="#000000" face="times new roman, new york, times, serif" size="2"><i><font color="#000000" face="arial, helvetica, sans-serif" size="3">-------------------------------------------------<br><br></font></i></font></i></div><div style="font-family:HelveticaNeue,"Helvetica Neue",Helvetica,Arial,"Lucida Grande",sans-serif;font-size:16px"><font color="#000000" face="times new roman, new york, times, serif" size="2"><div align="left"><font face="arial, helvetica, sans-serif" size="3"><font color="#000000" face="times new roman, new york, times, serif" size="2"></font></font></div></font></div></div></font></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div><br></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Thu, Aug 13, 2020 at 11:55 PM David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
  
    
  
  <div>
    <p>Dr. Bina,</p>
    <p> There are two kinds of division by zero errors. If you're
      getting one that is being reported by TRNSYS in the error/warning
      log then make sure that any equations you have in your input file
      are written like:</p>
    <p>myEquation = 1/MAX(myVariable,0.)</p>
    <p>The other kind of division by zero error is an ugly unhandled one
      that comes up in a popup window over top of your online plotter.
      If that is the kind that you are getting then please send the
      project and any additional files needed to run it to your
      distributor. They'll need to get into the code to find the cause
      of the error.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div>On 08/13/2020 09:40, saeid
      mohammadzadeh wrote:<br>
    </div>
    <blockquote type="cite">
      
      <div dir="ltr">
        <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">Dear
          Dr. David;</div>
        <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">Thank
          you so much for your reply. I finally found a way but still
          does not work for the cooling condition. I made seasonally and
          hourly forcing files and connected them as an input file to my
          building (as you mentions in this email also). But
          unfortunately for cooling give the error of division by
          zero...</div>
        <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">Another
          way is using an excel file but again in the cooling does not
          work and I think it is because of the zeros in the days,
          weekends, and no airconditioning seasons.</div>
        <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
        </div>
        <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small"><i style="color:rgb(0,0,0);font-family:Arial,Helvetica,sans-serif;font-size:12.8px"><font size="2" color="#000000"><i><font face="arial, helvetica,
                  sans-serif" color="#000000">Best Regards</font></i></font></i></div>
        <div>
          <div dir="ltr">
            <div dir="ltr">
              <div>
                <div dir="ltr">
                  <div dir="ltr">
                    <div dir="ltr">
                      <div dir="ltr">
                        <div dir="ltr">
                          <div dir="ltr">
                            <div dir="ltr">
                              <div dir="ltr">
                                <div dir="ltr">
                                  <div dir="ltr">
                                    <div dir="ltr">
                                      <div dir="ltr">
                                        <div dir="ltr">
                                          <div dir="ltr">
                                            <div dir="ltr">
                                              <div dir="ltr">
                                                <div style="color:rgb(0,0,0)"><i><font size="2" face="arial,
                                                      helvetica,
                                                      sans-serif">Saeid
                                                      Mohammadzadeh
                                                      Bina, Dr. (Eng.)</font></i></div>
                                                <div style="color:rgb(0,0,0)"><i style="font-size:12.8px;color:rgb(34,34,34)"><font size="2" face="times
                                                      new roman, new
                                                      york, times,
                                                      serif" color="#000000"><i><font size="3" face="arial,
                                                          helvetica,
                                                          sans-serif" color="#000000">-------------------------------------------------</font></i></font></i></div>
                                                <div><font size="2" face="times
                                                    new roman, new york,
                                                    times, serif" color="#000000">
                                                    <div align="left"><font style="font-size:16px" size="3" face="arial, helvetica, sans-serif"><font size="2" face="times
                                                          new roman, new
                                                          york, times,
                                                          serif" color="#000000">
                                                          <div align="left"><em><font face="times
                                                          new
                                                          roman,serif">Akita
                                                          <var></var>University</font></em><br>
                                                          </div>
                                                        </font></font><font face="arial,
                                                        helvetica,
                                                        sans-serif"><font size="2" face="times
                                                          new roman, new
                                                          york, times,
                                                          serif" color="#000000">
                                                          <div align="left"><span style="font-family:"Times New Roman",serif"><i>Graduate
                                                          school of
                                                          International
                                                          Resource
                                                          Sciences</i></span><font face="times
                                                          new
                                                          roman,serif"><em>.<br>
                                                          1-1 Tegata
                                                          gakuen-machi,
                                                          Akita
                                                          010-8502,
                                                          Japan</em></font></div>
                                                          <div align="left"><font face="times
                                                          new
                                                          roman,serif"><em>Tel: </em></font><em style="font-family:"times new roman",serif">+815068665026
                                                          (Japan)</em></div>
                                                          <div align="left"><em style="font-family:"times new roman",serif">     
                                                           +989141011757
                                                          (Iran)</em><em style="font-family:"times new roman",serif">   </em></div>
                                                        </font></font></div>
                                                    <div align="left"><font style="font-size:16px" size="3" face="garamond, new york, times, serif"><em>E-mail: </em></font><a href="mailto:s.mohammadzadeh66@gmail.com" target="_blank"><em>d9515254@s.akita-u.ac.jp</em></a><em style="font-size:16px"> </em></div>
                                                    <div style="font-size:16px" align="left"><em> 
                                                                 <a href="mailto:mohammadzadehsaeid@yahoo.com" rel="nofollow" target="_blank">mohammadzadehsaeid@yahoo.com</a></em></div>
                                                  </font><font style="font-size:16px" size="2" face="times
                                                    new roman, new york,
                                                    times, serif" color="#000000">
                                                    <div align="left">
                                                      <div><i><font size="2" face="times
                                                          new roman, new
                                                          york, times,
                                                          serif" color="#000000"><i><font size="3" face="arial,
                                                          helvetica,
                                                          sans-serif" color="#000000">-------------------------------------------------<br>
                                                          <br>
                                                          </font></i></font></i></div>
                                                    </div>
                                                  </font></div>
                                              </div>
                                            </div>
                                          </div>
                                        </div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
        <br>
      </div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Thu, Aug 13, 2020 at 11:32
          PM David BRADLEY <<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>> wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div>
            <p>Dr Bina,</p>
            <p>  If you have access to the TESS Applications Library,
              you can define such schedules using the Types in that
              library. In TRNBuild you will need to select that the
              schedule values will come from INPUTS instead of from
              SCHEDULES that are defined inside TRNBuild.</p>
            <p>best,</p>
            <p> David</p>
            <p><br>
            </p>
            <div>On 08/12/2020 23:12, saeid mohammadzadeh via
              TRNSYS-users wrote:<br>
            </div>
            <blockquote type="cite">
              <div dir="ltr">
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">Hello
                  dear TRNSYS users;</div>
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
                </div>
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">I
                  have a question regarding the schedule for heating and
                  cooling:</div>
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">Firstly,
                  I want to calculate the heating and cooling loads
                  using the energy balance method (just on the heating
                  the cooling buttons) based on the following time
                  table:</div>
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">For
                  weekdays from 8 to 18 (either cooling or heating);</div>
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">For
                  the weekends off (either cooling or heating);</div>
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">From
                  Nov. to April "Heating"; </div>
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">From
                  Jul. to Sep. "Cooling".</div>
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">Secondly,
                  I would like to use this schedule and also
                  thermostat (either schedule or zone temperature is 1
                  for heating or cooling) to command the airconditioning
                  system that I will add later. </div>
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
                </div>
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small">And
                  another issue, which is not important now, on weekdays
                  later I want to use complex timing (8 to 18 full
                  occupancy and other hours ratio of office workers). </div>
                <div class="gmail_default" style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
                </div>
                <div>
                  <div dir="ltr">
                    <div dir="ltr">
                      <div>
                        <div dir="ltr">
                          <div dir="ltr">
                            <div dir="ltr">
                              <div dir="ltr">
                                <div dir="ltr">
                                  <div dir="ltr">
                                    <div dir="ltr">
                                      <div dir="ltr">
                                        <div dir="ltr">
                                          <div dir="ltr">
                                            <div dir="ltr">
                                              <div dir="ltr">
                                                <div dir="ltr">
                                                  <div dir="ltr">
                                                    <div dir="ltr">
                                                      <div dir="ltr">
                                                        <div style="color:rgb(0,0,0)"><i style="font-size:12.8px"><font size="2" color="#000000"><i><font face="arial,
                                                          helvetica,
                                                          sans-serif" color="#000000">Best
                                                          Regards</font></i></font></i><br>
                                                        </div>
                                                        <div style="color:rgb(0,0,0)"><i><font size="2" face="arial,
                                                          helvetica,
                                                          sans-serif">Saeid
                                                          Mohammadzadeh
                                                          Bina, Dr.
                                                          (Eng.)</font></i></div>
                                                        <div style="color:rgb(0,0,0)"><i style="font-size:12.8px;color:rgb(34,34,34)"><font size="2" face="times
                                                          new roman, new
                                                          york, times,
                                                          serif" color="#000000"><i><font size="3" face="arial,
                                                          helvetica,
                                                          sans-serif" color="#000000">-------------------------------------------------</font></i></font></i></div>
                                                        <div><font size="2" face="times
                                                          new roman, new
                                                          york, times,
                                                          serif" color="#000000">
                                                          <div align="left"><font style="font-size:16px" size="3" face="arial, helvetica, sans-serif"><font size="2" face="times
                                                          new roman, new
                                                          york, times,
                                                          serif" color="#000000">
                                                          <div align="left"><em><font face="times
                                                          new
                                                          roman,serif">Akita
                                                          <var></var>University</font></em><br>
                                                          </div>
                                                          </font></font><font face="arial,
                                                          helvetica,
                                                          sans-serif"><font size="2" face="times
                                                          new roman, new
                                                          york, times,
                                                          serif" color="#000000">
                                                          <div align="left"><span style="font-family:"Times New Roman",serif"><i>Graduate school
                                                          of
                                                          International
                                                          Resource
                                                          Sciences</i></span><font face="times
                                                          new
                                                          roman,serif"><em>.<br>
                                                          1-1 Tegata
                                                          gakuen-machi,
                                                          Akita
                                                          010-8502,
                                                          Japan</em></font></div>
                                                          <div align="left"><font face="times
                                                          new
                                                          roman,serif"><em>Tel: </em></font><em style="font-family:"times new roman",serif">+815068665026
                                                          (Japan)</em></div>
                                                          <div align="left"><em style="font-family:"times new roman",serif">     
                                                           +989141011757
                                                          (Iran)</em><em style="font-family:"times new roman",serif">   </em></div>
                                                          </font></font></div>
                                                          <div align="left"><font style="font-size:16px" size="3" face="garamond, new york, times, serif"><em>E-mail: </em></font><a href="mailto:s.mohammadzadeh66@gmail.com" target="_blank"><em>d9515254@s.akita-u.ac.jp</em></a><em style="font-size:16px"> </em></div>
                                                          <div style="font-size:16px" align="left"><em> 
                                                                   <a href="mailto:mohammadzadehsaeid@yahoo.com" rel="nofollow" target="_blank">mohammadzadehsaeid@yahoo.com</a></em></div>
                                                          </font><font style="font-size:16px" size="2" face="times
                                                          new roman, new
                                                          york, times,
                                                          serif" color="#000000">
                                                          <div align="left">
                                                          <div><i><font size="2" face="times
                                                          new roman, new
                                                          york, times,
                                                          serif" color="#000000"><i><font size="3" face="arial,
                                                          helvetica,
                                                          sans-serif" color="#000000">-------------------------------------------------<br>
                                                          <br>
                                                          </font></i></font></i></div>
                                                          </div>
                                                          </font></div>
                                                      </div>
                                                    </div>
                                                  </div>
                                                </div>
                                              </div>
                                            </div>
                                          </div>
                                        </div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
              <br>
              <fieldset></fieldset>
              <pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
            </blockquote>
            <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
          </div>
        </blockquote>
      </div>
    </blockquote>
    <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
  </div>

</blockquote></div>