<p>Dr. Bina,</p>
<p> There are two kinds of division by zero errors. If you're
getting one that is being reported by TRNSYS in the error/warning
log then make sure that any equations you have in your input file
are written like:</p>
<p>myEquation = 1/MAX(myVariable,0.)</p>
<p>The other kind of division by zero error is an ugly unhandled one
that comes up in a popup window over top of your online plotter.
If that is the kind that you are getting then please send the
project and any additional files needed to run it to your
distributor. They'll need to get into the code to find the cause
of the error.</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<div class="moz-cite-prefix">On 08/13/2020 09:40, saeid
mohammadzadeh wrote:<br>
</div>
<blockquote type="cite"
cite="mid:CABCqxALPtYmwnwvh2FMUBb=b6MEXjR3mpJdAoO8QZ6RPFjxsvg@mail.gmail.com">
<meta http-equiv="content-type" content="text/html; charset=UTF-8">
<div dir="ltr">
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">Dear
Dr. David;</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">Thank
you so much for your reply. I finally found a way but still
does not work for the cooling condition. I made seasonally and
hourly forcing files and connected them as an input file to my
building (as you mentions in this email also). But
unfortunately for cooling give the error of division by
zero...</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">Another
way is using an excel file but again in the cooling does not
work and I think it is because of the zeros in the days,
weekends, and no airconditioning seasons.</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small"><i
style="color:rgb(0,0,0);font-family:Arial,Helvetica,sans-serif;font-size:12.8px"><font
size="2" color="#000000"><i><font face="arial, helvetica,
sans-serif" color="#000000">Best Regards</font></i></font></i></div>
<div>
<div dir="ltr" class="gmail_signature"
data-smartmail="gmail_signature">
<div dir="ltr">
<div>
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div
style="color:rgb(0,0,0)"><i><font
size="2"
face="arial,
helvetica,
sans-serif">Saeid
Mohammadzadeh
Bina, Dr. (Eng.)</font></i></div>
<div
style="color:rgb(0,0,0)"><i
style="font-size:12.8px;color:rgb(34,34,34)"><font size="2" face="times
new roman, new
york, times,
serif"
color="#000000"><i><font
size="3"
face="arial,
helvetica,
sans-serif"
color="#000000">-------------------------------------------------</font></i></font></i></div>
<div
style="color:rgb(0,0,0);font-family:HelveticaNeue,"Helvetica
Neue",Helvetica,Arial,"Lucida Grande",sans-serif"><font
size="2" face="times
new roman, new york,
times, serif"
color="#000000">
<div align="left"><font
style="font-size:16px" size="3" face="arial, helvetica, sans-serif"><font
size="2"
face="times
new roman, new
york, times,
serif"
color="#000000">
<div
align="left"><em><font
face="times
new
roman,serif">Akita
<var></var>University</font></em><br>
</div>
</font></font><font
face="arial,
helvetica,
sans-serif"><font
size="2"
face="times
new roman, new
york, times,
serif"
color="#000000">
<div
align="left"><span
style="font-family:"Times New Roman",serif"><i>Graduate
school of
International
Resource
Sciences</i></span><font
face="times
new
roman,serif"><em>.<br>
1-1 Tegata
gakuen-machi,
Akita
010-8502,
Japan</em></font></div>
<div
align="left"><font
face="times
new
roman,serif"><em>Tel: </em></font><em
style="font-family:"times new roman",serif">+815068665026
(Japan)</em></div>
<div
align="left"><em
style="font-family:"times new roman",serif">
+989141011757
(Iran)</em><em
style="font-family:"times new roman",serif"> </em></div>
</font></font></div>
<div align="left"><font
style="font-size:16px" size="3" face="garamond, new york, times, serif"><em>E-mail: </em></font><a
href="mailto:s.mohammadzadeh66@gmail.com" target="_blank"
moz-do-not-send="true"><em>d9515254@s.akita-u.ac.jp</em></a><em
style="font-size:16px"> </em></div>
<div
style="font-size:16px"
align="left"><em
style="font-family:garamond,"new
york",times,serif;font-size:medium;background-color:rgba(0,0,0,0);margin:0px;padding:0px;color:blue">
<a
href="mailto:mohammadzadehsaeid@yahoo.com"
rel="nofollow"
style="font-family:garamond,"new
york",times,serif;font-size:medium;background-color:rgba(0,0,0,0);margin:0px;padding:0px;color:blue"
target="_blank" moz-do-not-send="true">mohammadzadehsaeid@yahoo.com</a></em></div>
</font><font
style="font-size:16px"
size="2" face="times
new roman, new york,
times, serif"
color="#000000">
<div align="left">
<div
style="font-family:HelveticaNeue,"Helvetica
Neue",Helvetica,Arial,"Lucida
Grande",sans-serif;font-size:16px"><i><font
size="2"
face="times
new roman, new
york, times,
serif"
color="#000000"><i><font
size="3"
face="arial,
helvetica,
sans-serif"
color="#000000">-------------------------------------------------<br>
<br>
</font></i></font></i></div>
</div>
</font></div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
</div>
<br>
<div class="gmail_quote">
<div dir="ltr" class="gmail_attr">On Thu, Aug 13, 2020 at 11:32
PM David BRADLEY <<a href="mailto:d.bradley@tess-inc.com"
moz-do-not-send="true">d.bradley@tess-inc.com</a>> wrote:<br>
</div>
<blockquote class="gmail_quote" style="margin:0px 0px 0px
0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
<div>
<p>Dr Bina,</p>
<p> If you have access to the TESS Applications Library,
you can define such schedules using the Types in that
library. In TRNBuild you will need to select that the
schedule values will come from INPUTS instead of from
SCHEDULES that are defined inside TRNBuild.</p>
<p>best,</p>
<p> David</p>
<p><br>
</p>
<div>On 08/12/2020 23:12, saeid mohammadzadeh via
TRNSYS-users wrote:<br>
</div>
<blockquote type="cite">
<div dir="ltr">
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">Hello
dear TRNSYS users;</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">I
have a question regarding the schedule for heating and
cooling:</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">Firstly,
I want to calculate the heating and cooling loads
using the energy balance method (just on the heating
the cooling buttons) based on the following time
table:</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">For
weekdays from 8 to 18 (either cooling or heating);</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">For
the weekends off (either cooling or heating);</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">From
Nov. to April "Heating"; </div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">From
Jul. to Sep. "Cooling".</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">Secondly,
I would like to use this schedule and also
thermostat (either schedule or zone temperature is 1
for heating or cooling) to command the airconditioning
system that I will add later. </div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
</div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small">And
another issue, which is not important now, on weekdays
later I want to use complex timing (8 to 18 full
occupancy and other hours ratio of office workers). </div>
<div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
</div>
<div>
<div dir="ltr">
<div dir="ltr">
<div>
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div
style="color:rgb(0,0,0)"><i
style="font-size:12.8px"><font size="2" color="#000000"><i><font
face="arial,
helvetica,
sans-serif"
color="#000000">Best
Regards</font></i></font></i><br>
</div>
<div
style="color:rgb(0,0,0)"><i><font
size="2"
face="arial,
helvetica,
sans-serif">Saeid
Mohammadzadeh
Bina, Dr.
(Eng.)</font></i></div>
<div
style="color:rgb(0,0,0)"><i
style="font-size:12.8px;color:rgb(34,34,34)"><font size="2" face="times
new roman, new
york, times,
serif"
color="#000000"><i><font
size="3"
face="arial,
helvetica,
sans-serif"
color="#000000">-------------------------------------------------</font></i></font></i></div>
<div><font
size="2"
face="times
new roman, new
york, times,
serif"
color="#000000">
<div
align="left"><font
style="font-size:16px" size="3" face="arial, helvetica, sans-serif"><font
size="2"
face="times
new roman, new
york, times,
serif"
color="#000000">
<div
align="left"><em><font
face="times
new
roman,serif">Akita
<var></var>University</font></em><br>
</div>
</font></font><font
face="arial,
helvetica,
sans-serif"><font
size="2"
face="times
new roman, new
york, times,
serif"
color="#000000">
<div
align="left"><span
style="font-family:"Times New Roman",serif"><i>Graduate school
of
International
Resource
Sciences</i></span><font
face="times
new
roman,serif"><em>.<br>
1-1 Tegata
gakuen-machi,
Akita
010-8502,
Japan</em></font></div>
<div
align="left"><font
face="times
new
roman,serif"><em>Tel: </em></font><em
style="font-family:"times new roman",serif">+815068665026
(Japan)</em></div>
<div
align="left"><em
style="font-family:"times new roman",serif">
+989141011757
(Iran)</em><em
style="font-family:"times new roman",serif"> </em></div>
</font></font></div>
<div
align="left"><font
style="font-size:16px" size="3" face="garamond, new york, times, serif"><em>E-mail: </em></font><a
href="mailto:s.mohammadzadeh66@gmail.com" target="_blank"
moz-do-not-send="true"><em>d9515254@s.akita-u.ac.jp</em></a><em
style="font-size:16px"> </em></div>
<div
style="font-size:16px"
align="left"><em>
<a
href="mailto:mohammadzadehsaeid@yahoo.com"
rel="nofollow"
target="_blank" moz-do-not-send="true">mohammadzadehsaeid@yahoo.com</a></em></div>
</font><font
style="font-size:16px"
size="2"
face="times
new roman, new
york, times,
serif"
color="#000000">
<div
align="left">
<div><i><font
size="2"
face="times
new roman, new
york, times,
serif"
color="#000000"><i><font
size="3"
face="arial,
helvetica,
sans-serif"
color="#000000">-------------------------------------------------<br>
<br>
</font></i></font></i></div>
</div>
</font></div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
<fieldset></fieldset>
<pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank" moz-do-not-send="true">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<pre cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank" moz-do-not-send="true">d.bradley@tess-inc.com</a>
<a href="http://www.tess-inc.com" target="_blank" moz-do-not-send="true">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank" moz-do-not-send="true">http://www.trnsys.com</a></pre>
</div>
</blockquote>
</div>
</blockquote>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>